Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


I have connected 04nos. earthings to a transformer through
04nos. earthing pits seperately. 02nos. earthings are
connected to T/F body, and 02nos. earthings are connected to
T/F neutral.T/F capacity is 2000KVA, 11KV/415V. But after
completing of 02 years successful operation ,we are
facing following problems-

1. CT/PT occured blast one time
2. HT cable box occured blast two times
3. One body earthing strip and one neutral earthing strip of
transformer are overlapping at some places. Whenever these
two strips are pressed at overlapped points, they made spark.

What is the reason of spark?

Please explain the reason & rectification of above problems

Answers were Sorted based on User's Feedback



I have connected 04nos. earthings to a transformer through 04nos. earthing pits seperately. 02nos. ..

Answer / k.bhaskar

I think your neutral earth pits resistance is not
good,ensure each earth pit resistance with out grid.The
reason for sparking may be body earth is good and some
potential is there in the neutral path.

Second ensure transformer core channel to earth connection
(inside).Measure the winding resistance and unbalance load
distribution may also cause developing voltage in Neutral.

Is This Answer Correct ?    2 Yes 0 No

I have connected 04nos. earthings to a transformer through 04nos. earthing pits seperately. 02nos. ..

Answer / ullas

the answer follows.
1. ct/pt unit blast doesn't relate with the problem. it may
due to its poor quality , or some other reasons.
2. ht cable end box blast can be occured in so many ways.
may be due to rain water entered in to the end box leading
to short circuit the phases.
or due to poor quality,etc maybe the reason.
you can do one thing.
please disconnect the earthing of ht cable armour either at
transformer side or at the double pole structure.
3. this sparking indicated that your transformer neutral is
no longer maintains zero potential.
so please first measure the voltage of neutral.
this is done by inserting a spike five meters from the
transformer and take this terminal as earth terminal of
zero potential. and between this terminal and transformer
neutral measure the voltage developed.
if it is indicating a sufficient voltage, then it is true
that your neutral is shifted from its zero position.
if there is any fuse used in the neutral circuit, change
it in to a link.
check the whole circuit for any abnormal conditions.

Is This Answer Correct ?    1 Yes 0 No

I have connected 04nos. earthings to a transformer through 04nos. earthing pits seperately. 02nos. ..

Answer / santosh kawade

Please contact me Santosh 9224 69 3116,

Probably site inspection require to sortout your problem.

Is This Answer Correct ?    1 Yes 1 No

I have connected 04nos. earthings to a transformer through 04nos. earthing pits seperately. 02nos. ..

Answer / elangeswaran

pl check the type of load connected and if the secondary is
feeding a system of two sources with a buscoupler(three
pole) and neutral interconnected bus ultimatly neutral
voltage is above allowable level.

Is This Answer Correct ?    0 Yes 0 No

I have connected 04nos. earthings to a transformer through 04nos. earthing pits seperately. 02nos. ..

Answer / siva kumar

because of improper earthing the transformer neutral voltage may raise to abnormal level and may cause failure of CT/PT sets.
The star point you made on secondaries of CT, should be made at the equipement only and connected to earth to avoid transfer potential.
If you have not integrated your earth pits,
connect all the four earth pits with 50X8 GI flat.
now check earth pit resistance is with in limits.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what is meant by insulation voltage in cables? explain it?

4 Answers   ABB,


HOW EFFICIENTLY LOAD IS SHARED BETWEEN ALTERNATORS

1 Answers  


what objective books are good for preparing for PSU's?

3 Answers   NTPC,


HOW TO FIND OUT 1. LINE CURRENT, 2. PHASE CURRENT IN AN ALTERNATOR / TRANSFORMER WHICH IS FEEDING A I)STAR LOAD ii) DELTA LOAD, USING A CLAMP METER. NORMALLY WHEN WE USE CLAMP METER IN A DG SET THEN WHAT DO WE GET?? PHASE CURRENT OR LINE CURRENT.

13 Answers   Bhel,


How can decide the MVA rating of power transformer for substation like 220/132, 132/66, 66/33kv etc or even higher kv rating of substation???? Send me the strictly technical answer that shows your strong technical aptitude.

6 Answers  


i need online ups battery calculater

1 Answers  


What is Isolation Transformer???

4 Answers   Emerson,


What is I to C?

0 Answers   PowerTech,


What is RMU, and what it's function?

2 Answers  


A 7 storey building has a floor area of 35,000sq.ft on each storey. On the ground floor 11KV electrical sub-station is to be erected. A load of 3kw for every 400sq.ft (p.f is 0.8) is proposed for each floor. fire pump 7.5hp, water pump 5hp, lift 2 nos, each 10hp and 20shop load of each shop is 5kw. calculate a. load each floor b. total load of building c. L.T feeders for aech floor and from transformer to main. d. distribution diagram e. capacity of sub-station/capacitor bank f. line diagram

0 Answers  


What is EOL?

1 Answers  


why CT output is always raetd 5.regardsof primery curre.

3 Answers   ABB, BARC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)