Answer / jccarlisle
An I/P transducer is a device which converts a current
signal (usually 4-20mA) to a pneumatic signal (pressure
depends on actuator size requirement). The pneumatic signal
goes either directly to control device (valve, damper, etc)
for operation of the device or to a positioner which
measures the amount of mechanical travel of the control
device and adjusts the input until the exact percentage of
movement called for is achieved.
An E/P is a device that integrates both devices above into
one unit.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / pavan
i think i/p
converter
converts current
in to
pressure,where e/
p converter
converts voltage
to pressure.
| Is This Answer Correct ? | 3 Yes | 6 No |
Answer / somaraju
if varing voltage with a constant current it is E/P
if varing current with constant voltage it is I/P
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / mike betts
My understanding that the IP positioner would be that you
are using a current signal (I) and converting it to a
pressure signal (P) in order to operate a positioner valve.
I would call the signal conditioner in this case an I to P
converter.
I am not so sure about EP, but E can be used to mean EMF
which is measured in volts and so could ve voltage to
pressure signal conditioner in the same way as I to P in
the example above.
| Is This Answer Correct ? | 19 Yes | 26 No |
Answer / dennis
The "E/P" elector-pneumatic positioner is used for
operation of pneumatic rotary valve actuators by means of
electroller or control systems with an analog output signal
of "DC4 to 20mA" or split ranges.
I/P not sure yet.
| Is This Answer Correct ? | 2 Yes | 11 No |
Answer / rahul dhumal
E/P is combination of I/P & positioner i.e. the o/p pf E/P is directaly given to the valve actuator.
And in the case of I/p 4-20ma is given to it & output of I/P is given to the positioner .
| Is This Answer Correct ? | 14 Yes | 24 No |
Answer / s.m.patel
I to p means input signal is 4-20MA
E to p means input signal is 0 to 10 VDC
| Is This Answer Correct ? | 7 Yes | 19 No |
why we are using digital signals for I/O & how to measure this signals is getting or not ?
can we control operation of PLC from operator station?
how can leve transmetter calibate in feild .and also put cv and flow plz .....
Is that Speed Probe and Vibration Probe sensors are same,if yes what is the diff b/w them?
How to get Cv of control valve having following parameter ,i.e inlet pressure 4.5kg/cm2 outlet pressure 1 kg/cm2 specific gravity 0.808
what is wave length were using ?
what is 24vdc live and dry supply
which type of zones used for boiler? & why ?
When cryogenic control valve will be applied?
what is mean by TDC-3000
Is it possible to convert 4 wire transmitter to convert to 2 wire with additional relay.Please send detial with drawing,i will appreciate.
HOW THE ORIFICE & PRV SIZING BE HAPPENED -- EXPLAIN IN BRIEF
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)