1)What will you do if main incomer VCB fail in your site ?
Answers were Sorted based on User's Feedback
Answer / vijay chander
first we informed to respective electricity office and then
find the fault inside the VCB or E.B side. if inside the
VCB means call the person from VCB manufetures.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / sskumar
Hai everybody,
Good and thanks to all of you for giving a ideas.But here
we should discuss only Technical matters not for
management.
So coming to the point, first we should cut off the
incoming supply to the VCB, how? first we should open the
AB switch, then automatically the supply wont come to VCB.
Then remove the VCB and rectify it.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / gunasekaran
if we have double bus system we can close the B/C unit and
get the supply from another bus
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / kanand078
if DG is there run the pland at dg load..after i will check
the fault and rectify
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / y.hari kishore babu
first we should cut off the incoming supply to the VCB, how?
first we should open the AB switch, then automatically the
supply wont come to VCB.
Then remove the VCB and rectify the problem by vendor or
myself with help of our tecnicians
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / g.kumaresan.
If Main incomer fail in our site Immediatly to Isolate the
incomming supply and VCB. Bec's to protect the inside Heavy
Equipment insite in our site, then to inform the situation
in our Authoriy officer, at the same time to ensure the
back feeding arrangement, Bec's can not maintain the supply
intruption in long time.
So, doing back feeding arrangement immediatly with our
higher authrity knowledge and also other officer sugection.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / anish salvi
If the incomer is further joint to transmission line Than no worry!! just Bypass the CB beacuse there are always CTs & pTS for the measurement purpose & in case if any fault occurs than even in absense of the Vaccum circuit breaker (used for 110KV and above)
Where as if it is the Distribution than use DO fuse for protection
| Is This Answer Correct ? | 0 Yes | 0 No |
what is diode? and what it is used for ?
What is the criteria for selecting the voltage classes of an AC Induction Motor.The KW rating above/below which ht/lt selection is made may be provided in details.
If the earth is a good conductor of electricity, why don't people get shocked every time they walking on earth?
How to decide the rating of CBCT? We have 6.6Kv switchgear & having 50/1 cbct ,i want to know how this 50/1 A came? On what basis we decide CBCT reting?
Thumb rule for capacitor bank calculation
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The slip when motor stalls is A 1 B 0 C 13.33% D 10.33%
For testing 33kv cable hipot testing. How much kv we have to Apply .Give in details.
What is difference between A.C & D.C Resistance ?
Why is the generator rating always in kVA and motor rating in kW?
11000volt DG set carnt kaise banvay
why not phase to phase fault occure in raining day in hv sub-station?
where we use compound motors in real time and why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)