What is difference between A.C & D.C Resistance ?
Answers were Sorted based on User's Feedback
Answer / ashok
There is no polarity for resistance. In AC consider voltage
and in DC current should be consider
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / dileep t
The A.C resistance is always greater than D.C resistance.
A.C resistance is about 1.62 times D.C resistance. In D.C
the frequency is zero . Hence the total impedance of a line
will be only resistive.
z=R+XL
since f=0;XL=0
Z=R.
But in A.C f is not equal to zero. Hence Z will be large as
compared with D.C
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / suresh
d.c resistance is only resistance due to the virtue of
conductor property only, a.c resistance is due to both
virtue of conductor property and skin effect.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / blade
In AC the movement of electric charge periodically reverse.
In DC the movement of electric charge is only in one
direction.
Is This Answer Correct ? | 5 Yes | 5 No |
Why in 6 KV XLPE cable termination kit used and why not in 380 V xlpe cable same is not used
what are the effects of variations in frequency when you are connected to national grid??
what do you mean by earth fault in transformer?
whether inrush current for lamps or capcitors should be considered cable sizing to feed that load.
We use MCCB not MCB for motor starters because MCCBs has capablity to drawout the motor starting current which is 5-6 times the full load current of motor for 1sec. Then why we use SDF in starter panel means MCC panels. Pls reply if any one knows this answer.
An automatic water heater is an example of which type of control system?
how braking & making capacity of circuit breaker is calculated?
how we design a pannel to start 10HP motor with the help of star delta starter?
What is mean by earthed & unearthed cable? Voltage grade of 1.9/3.3 kV(E), 3.3/3.3 kV(UE), 3.8/6.6 kV(E)what it indicates??
why nearly all the voltage levels are in the multiples of 11 like 3.3 ,6.6 ,33 ,11 kv.....
PRV (Pressure relief valve) Trip with oil splash outside power transformers
We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Make Atlas Copco 5.5 kva) that time we face the lot of fluctuation on Dg output. Can you please suggest me how can prevent this fluctuation?