what is the procedure to carry out BDV test of a
transformer ?
Answers were Sorted based on User's Feedback
Answer / p.s.suresh
1. first we will take filltered oil in test kit.
2. then maintained 2.5mm gap between electrode and applying
rated 40 & 60 Kv for 1 minite .
3. the above test withstood for 1 minite its ok for
energiseing the transformer.
Is This Answer Correct ? | 22 Yes | 9 No |
Answer / c.b.sharma
1.first we will take filltered oil in test kit.
2. then maintained 2.5mm gap between electrode and applying
rated 40 & 60 Kv for 1 minite .
3. the above test withstood for 1 minite its ok for
energiseing the transformer.
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / vinod
1)Take transformer oil sample from both bottom and top
section with suitable container on dry day
2)Adjust the BDV kit electrode for 2.5 mm and ceck with
gauge, increase the voltage till breakdown occur
3)Now a day automatic tester is available it will take
consicutive five readings with stiror. third reading will
be the BDV.
Is This Answer Correct ? | 8 Yes | 3 No |
what is the difference between inverter and ups & what is the earth resistance for ups , if its high why so
Write the force balance equation of ideal dashpot element.
We have 2 Nos. Transformer with the capacity of 2000KVA and 1250 KVA and currently using only one 2000KVA T/R during operational hours while non- operational hous 1250 KVA T/R also used to reduce T & D losses. Similarly, 2 capacitor bank of 500KVAR and 300 KVAR also installed to balance reactive power. Now problem is around 1000 KW load PF is not maintaning 0.99 as 350 KVAR capacitor is in healty condtion. Now the PF is maintain 0.95 to 0.96.
What are the drawbacks of HVDC system?
Why are short circuit ratings always 16kA,25kA,36kA and 50kA.Who has fixed these?
In a transformer ,when voltage decreases current increases. but this is a violation of oms law.why?
When i went to a interview the interviewer ask me a question for that i cant able to answer him if anyone knows answer me How will you design a capacitor bank for a plant? if my p.f is 0.6 i have to improve it to 0.9 or 1 what kind of steps i have to do? and is there any formula for calculating this?
sir, Two different rating of generator going to connect parallel, can it set same DROOP or different. Why? Please explain
why motor rating in kw?
plz tell me Motor IP formula
why in 3.5 core means 3 core for phase and .5 for neutral?
how to select overload-relay for perticular motor 1.for D.O.L. starter 2. for Star-delta starter ????