How to calculate the ups battery back up? give the formula.
Answers were Sorted based on User's Feedback
Answer / ananth
T = N.V.X / VA
T= Time in Hours
N = No. of batteries
V= Voltage of Battery
X= Amp-Hour of the Battery
VA= Load
Is This Answer Correct ? | 156 Yes | 29 No |
Answer / subir kumar manna
numbers of battery * ah of battery /output kva*130
34*200 /160*130
6800/20800
0.32 hours .
Is This Answer Correct ? | 93 Yes | 48 No |
Answer / bhushan
UPS / Invertor Battery Backup Time =
----------------------------------
Batt Voltage X No.of (Batteries) X Ah (Single Battery) /
Total Load (Watts) = No.Hours Backup
Example :- 12v X 20(Batteries) X 200Ah (Single Battery)
/ 6000 (Watts) = No.Hours Backup
48000 / 6000 Watts = 8 Hours Backup
Is This Answer Correct ? | 55 Yes | 14 No |
Answer / a. dutta
To get one hour battery backup:
BATTERY AH = 1000 × VA × PF /( NO. OF BATTERY × BATTERY
VOLTAGE × LOAD% × PF
Is This Answer Correct ? | 27 Yes | 6 No |
Answer / sayyed fayyaz ahmed
Calculating the UPS and Battery Backup Time
Before calculating the Battery Backup, let us know a few
factors that vary battery backup.
For and UPS with 875Va we can us a maximum load of 640
watts 677Va we can us a maximum load of 540 watts
The main thing we should understand is that whatever may be
the UPS wattage the battery backup will not vary.
The battery backup will only vary depending on the battery
Ah and the Usage Load.
To calculate UPS backup, we have a simple formula.
UPS Backup = Battery Ah * (Volts/Load) * (1/Power Factor)
Example: Let us calculate the backup for a system UPS
Load is the usage power, suppose we are running a PC then
the load is around 300 watts
Power Factor varies for device to device, the average power
factor is 1.4
Voltage is the voltage of the battery.
For a single battery the voltage is 12v.
If the batteries are connected in a series Voltage = 12 *
no. of batteries.
Battery Ah is the battery ampere used for the ups,
System UPS battery AH is 7
Then Battery Backup = 7 * (12/300) * (1/1.4)
= 7 * (0.04) * (0.7)
= 0.19 hours
= 11.4 Minutes
Note: You can use the same formula for calculating the
battery backup for home UPS or an INVERTER.
Is This Answer Correct ? | 19 Yes | 12 No |
Answer / narayanarao.s
back up( in hours)= system dc volts x AH rating(
battery)/kva(load)x system power factor.
Is This Answer Correct ? | 11 Yes | 5 No |
Answer / balajiram
Time=ups efficiency*battery efficiency*battery low volts*battery AH/ups output(watts)
Is This Answer Correct ? | 14 Yes | 12 No |
Answer / prabhu
Battery Backup= No.of Batteries X Voltage of the batteries X Capacity of the batteries X Pf (0.8) / Load in Watts
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / prakash dhanshetty
backup time=(kva rating*power factor)!dc low of system
Is This Answer Correct ? | 8 Yes | 8 No |
what is thresold of perception
what is power factor ? how we can calculate the low power factor and amount of capacitor for improve that low factor ?
Best way to measure the Soil resistance of rocky soil, three probe method and four probe method
i have done my b.tech in 2009 .still hunting for a job...wat shud i answer if intervevwr asks..(what u have done 1yr)
HOW MUCH CURRENT CAN CARRY A 50 kvar DELTA CAPACITOR BANK?
why CT out put is 5 what ever the primary current.
how many types control panel of a 132/33 kv substation
HT and LT cables can be laid on same cable tray
whats relation b/w motor current & friqency
iam interesting to design the control panel for 3 phase pump motors by controling single phase switches.iam plan to use fuse,contactor & relay for motor protection .how can i select the voltage & amps rating for fuse,contactor & relay plz guide me .if anybody clarify my doubt means it will more helpful for my future .
When we need up only in o/p 440v, so why we use directly in 11kva in input?
0 Answers Lupin, Medhaj Techno Concept,
what is the difference between main meter CT and check meter CT?and what is the difference between main meter PT and check meter PT?