Answer / sureshbabu
for the grid connected system the earthing value must be
below the limit of 1 ohm
for the individual connected system the earthing value must
be less than 5 ohms
this is the IEC standard for earthing and bonding
Is This Answer Correct ? | 21 Yes | 1 No |
Answer / k.prakashchandra
In case of stations ,the maximum recommended values are
33KV-5 ohm, 66 KV -2, 110 to 400- 1.0 and generating station
-0.5.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mohan babu bommu
there is no hard and fast rule in large sub stations 1ohm small substatioms 2ohms ither places up 6ohms permissable
Is This Answer Correct ? | 0 Yes | 0 No |
What will be the full load current of 60KVA UPS. Suggest for this formula.
why the making current is more than then the breaking current and if its true then its about a controling circuit or breaker power contact points
How can get elongation of 2 k.G aluminium, if elongated aluminium dia is 2.5 mm?
differentiate between c curve and d curve MCBS?
What are the protections to be used for Generator?
All the socket in a room become very hot, the Wall was also became very hot and the earth conductor also became live, what in your view might be the possible causes?
what you mean by frequency of an igbt& how to find it?
what is the use of power transformer in GSS.
0 Answers College School Exams Tests, DLF, TCS,
what is the difference between RMS & TRUE RMS VOLTAGE
1.4 What is meant by CT knee point voltage and how would you determine it
1.WHAT ARE TRANSMISSION LINE LOSSES DURING WINTER AND SUMMER SEASON? 2.WHAT ARE THE CAUSES/ 3.WHEN THE CORONA IS MORE?.,WHETHER WINTER OR SUMMER? 4. WHAT IS THE PERCENTAGE OF LOSSES IN TRANSMISSION LINE?