Why is starter necessary for a three-phase induction motor?
Answers were Sorted based on User's Feedback
Answer / farha
A starter is needed for a three phase induction motor
because at the time of starting, if induction motor is
started directly, it will draw large amount of current
which causes damage to adjoining equipments.
Thus, a starter is needed in order to limit the starting
current.After the motor has started at reduced starting
current and hence reduced voltage, the connections are
diverted towards the mains supply so that now, the motor
can run at higher starting current and voltage.
Four types of starting methods are employed:
1.Star-Delta
2.Auto transformer method
3.Primary resistor starting.
4.Direct On-line.
Low rating upto 7 H.P motors can be started directly.
| Is This Answer Correct ? | 608 Yes | 51 No |
Answer / jessy
By starting an induction motor with starter limits the
starting current and starting torque .
Note - Upto 5 to 7.5 HP Three phase induction motors
generally started direct on line .
| Is This Answer Correct ? | 235 Yes | 51 No |
Answer / saurabh
at the time of starting slip S= 1, so the rotor resistance
which depends on slip i.e.
R2(1-S)/S will be equzl to "0",
i.e. rotor will act as short circuit.
hence initailly motor will draw heavy amount of current.
So in order to reduce this inrush current(5 to 7 times of
rated current), we apply less input voltage at the time of
starting so that input curent will be low(as in case of
star connection) & after some time or specified time input
will be fed in Delta connection.
if u understand this then ok other wise read more books in
details...
| Is This Answer Correct ? | 164 Yes | 24 No |
Answer / g.v.suresh kumar
AT THE STARTING OF THREE PHASE INDUCTION MOTOR THE STARTING
CURRENT IS HIGH IT IS DUE TO AT THE STARTING THE BACKEMF IS
0.SO BY USING STARTER WE CAN LIMIT THE STARTING CURRENT
| Is This Answer Correct ? | 146 Yes | 57 No |
Starter is used to reduce starting current.starting current
is usually large because of inertia,charecteristics of
motor winding(at starting slip=1,rotor resistance low
implies less back emf).So at starting we use starter .for
example.STAR DELTA starter.by using a starter at least the
switching is improved which is much important for safe and
longer life time use.simply a DOL can be used for lower
rated motors (up to 07 HP)in this case.for higher rated
motors (up to 15 HP)we can use a star delta connection.a
delta connected motor takes 1.7 times line current than a
star connectd motor.think ! at starting the current is
almost halved .Now a days we use drives (power electronics
products which not only takes care of starting of a motor
(improving power factor) also controls it as perrequirement.
| Is This Answer Correct ? | 56 Yes | 8 No |
Answer / patanjali
1--it limit the starting current.
2--increase the starting torque.
| Is This Answer Correct ? | 75 Yes | 32 No |
Answer / bhavik parekh
starter is reqired for the purpose of reduce starting
current. starting current reduce in starting period so that
starting torque is increase. another thing is that if
starter is not provided than high amont of current flow in
starting beacuase of that it may be chances to damege
itself and alose its adjoining m/c.
| Is This Answer Correct ? | 41 Yes | 18 No |
Answer / balasivakami
starter is required to limit the high starting current
| Is This Answer Correct ? | 32 Yes | 10 No |
Answer / monika khatri
when the induction motor starts.slip i.e "s" has a value
1...and hence the internal resistance value becomes
0..since resistance is directly proportinal to (s-1)....as
the resistance becomes 0..according to ohms law current
becomes very high.....tha value of current is about 5 to 6
times the full load curent......therefore the motor must
accelerate to high speed ,,which is not possible at "load"
condition.....and hence the motor may burst due to
overheating.............to prevent the motor from bursting
by reducing the value of current we use a STARTER....
| Is This Answer Correct ? | 24 Yes | 9 No |
what are ABCD curves in MCBs and how we observe that curves?
what are the points to be consider for MCB(miniature circuit breaker selection?
how do you test the capacitor bank ?
calotropis is an example of the following phyllotaxy
i want to trigger ATS (Mains +Generator )from external system could any body help me in this regard ?? is it posible if yes please tell me how?
Dear Sir / Madam, Actually we requied 64 A MCB, But i have 32 A MCB = 2 No's this two i have to make series connection and we usw any place? isit possible or not......
4 Answers Hindustan Unilever Limited,
If any HVDC line is going with positive & negative(the negative usually have return path of current with earthing electrode). Now the question is if this HVDC earthed electrode which is using as return path and earthed any nearby 400kv or 220kv AC substation equipments. which will be the impact of this on AC substation & its equipment, how severe may be this and what should be the minimum distance require between HVDC earthed electrode and AC substation equipments? It's really an high engineering level question...Dare to answer and increase your knowledge.
why HT motors are earthed only at equipment side & for it's single core cable with aluminium wire armoure using?
1 Answers Legrand, NLC Neyveli Lignite Corporation Limited,
what is the function and use of oil filled cables specify its advantages and disadvantages
in case of OC+EF relay, how the burden is divided/calculated/shared by the CTs in case of normal (healthy condition) and during fault conditions.? three coils of OC & ef coil is conected in residual connection across the three CTS.
What happens if a +vely charged particle is placed in the centre of a room and assume that the north side wall is having magnetised with north polarity and south side wall is magnetised with south polarity. In which direction the particle will move
Please let me know when replacing electromechanical Relays for protection of generators with sr489 multilin Relay, then there is no need to use 86 master trip relay Too. I am wondering this multilin relay has no contact to Stop breaker reclosing as 86 does
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)