Dear Sir / Madam,

Actually we requied 64 A MCB,

But i have 32 A MCB = 2 No's

this two i have to make series connection and we usw any
place?

isit possible or not......

Answers were Sorted based on User's Feedback



Dear Sir / Madam, Actually we requied 64 A MCB, But i have 32 A MCB = 2 No's this two ..

Answer / sagar

NO.
Because
MCB is used for over current protection.
you require 64A MCB for protection.
now if you will use 2 MCB of 32 A , then both the MCB will give protection for 32 A and will trip at 32 A.
so , you can't use the 32 A MCB in place of 64A MCB

Is This Answer Correct ?    21 Yes 1 No

Dear Sir / Madam, Actually we requied 64 A MCB, But i have 32 A MCB = 2 No's this two ..

Answer / hemant

if u connect 2 mcb's in series then it share load up to 32
amp only not for 64amp. if u used this two mcb then u must
to divided load in to two section like 32/32 amp. after
then u can connect load to out going terminals of mcbs.

Is This Answer Correct ?    14 Yes 0 No

Dear Sir / Madam, Actually we requied 64 A MCB, But i have 32 A MCB = 2 No's this two ..

Answer / nur.asidik

you can do that, but in parallel. not in series 

Is This Answer Correct ?    3 Yes 0 No

Dear Sir / Madam, Actually we requied 64 A MCB, But i have 32 A MCB = 2 No's this two ..

Answer / harikesh yadav

MCB USE ONLY LOW TENSON THIS RANGE 6AMP. TO 63 AMP.

VCB USE ONLY HIGH TENSON LINE FROM 2000AMP TO 4300 AMP.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

EXPLAIN WORKING PRINCIPLE OF ALTERNATOR & MOTORS.

2 Answers   L&T,


why neutral and earth should not be connected on 3 phase 440v/50c/s supply at consumer side. where as on 25kv/ac/50c/s railway traction substation neutral and earth will be connected and track at substation. and track will act as neutral and earth. Reasons for this is needed urgently

4 Answers  


HOW can i REuse the fused MLL LAMPS & GLS LAMPS at our factory

0 Answers  


We have laid the single core Armoured cable 7 nos ( 2 each phase & 1 neutral ) to cater our electrical load . the issue is though we have Glanded the cable both the end also givan the earthing to the panel both the end we are facing a heavy sparking at the gland side. what could be the reason.

12 Answers  


If one lamp connects between two phases it will glow or not?

0 Answers  






Why Motors are generally supplied with 3 core cables??? why not 4C??

5 Answers  


my UPS is 600VA with 0.6 p.f and i use it for my computer which has 450W power supply unit, a monitor of 633nW and speakers. Can any one explain this.. because the output of UPS should be 360W (<450W)

2 Answers  


low voltage grounding is done by?? 1)solidly gnd 2)ressistance 3)reactance

1 Answers  


What is the diffrence between an ELCB(earth leakage circuit breaker) and RCCB(residual current circuit breaker)?which has higher degree of safety and why?

2 Answers  


How to create a SCADA diagram on PC? I run the DG everyday but i dont know how that animated single line diagram is created.Please answer.

1 Answers  


if we convert watt into kva,which one formula use by us,pls tell me?

16 Answers   ABB,


What is the height of DA, DAL, DB, DC & DDE tower?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)