Answer / raja
Type B :
MCBs react quickly to overloads, and are set to trip
when the current passing through them is between 3 and 4.5
times the normal full load current.
Type C :
MCBs react more slowly, and are recommended for
applications involving inductive loads with high inrush
currents, such as fluorescent lighting installations. Type C
MCBs are set to trip at between 5 and 10 times the normal
full load current.
Type D :
MCBs are slower still, and are set to trip at between
10 and 20 times the normal full load current. They are
recommended only for circuits with very high inrush
currents, such as those feeding transformers and welding
machines.
Type A:
i have no idea on it
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / janet roadway
There is no A curve type within the IEC 60898 product
standard. The standard curves are B, C and D
Type B :
MCBs are set to trip when the current passing
through them is between 3 and 5 times the normal full load
current. The calibration temperature of this full load
current can vary from manufacturer but is generally in the
region of 30 - 40 degrees Celcius to allow for the heat
generated by the MCB within a distribution board.
Type C :
MCBs react more slowly, and are recommended for
applications involving inductive loads with high inrush
currents, such as fluorescent lighting installations. Type C
MCBs are set to trip at between 5 and 10 times the normal
full load current. Temperature as above
Type D :
MCBs are slower still, and are set to trip at between
10 and 20 times the normal full load current. They are
recommended only for circuits with very high inrush
currents, such as those feeding transformers and welding
machines. Temperature as above.
Some manufacturers produce their own specialist curves -
such as the ABB 'K' Curve which are designed for specific
applications such as tranformer feeds and motors. These
curves can be very useful.
| Is This Answer Correct ? | 1 Yes | 0 No |
We have 5 Distribution sections with variable loads&We have 3 Gensets(500kva,380kva&250kva) our total load is between 400kva to 600kva. so how could we connect 3gensets.
What is majour reason of Electrical Arcing ?
WHAT IS THE WINDING PROCEDURE OF ELECTRICAL MOTOR
Why insulation layer of a High Voltage cable is more than a current carrying cable?
what is over cureent protection
do we convert single phase line to three phase at minimum cost?
What is thef ormula to calculate the rating of a capacitor for a single phase motor
What is d role of reactive power in power system??How it produce & consume?
What is the Working principle of ELCB and RCCB?
Why shunt Generator is not recommended to start at ON LOAD condition???
ow can i get certificate of competency as electrical supervisor and my diploma in electrical engineering from jalgaon.
Define steady state error.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)