Answer / sakthivel.k
MCB- This it self says that Miniature Circuit Breaker.
MCB's ranges from 1Amps to 63Amps.
MCB's breaking capacity 10KA,15KA & 25KA.
MCB's occupies less space.
MCB's can be used even in the houses.
MCB's can be used with out enclosures but this is safer.
Whereas
MCCB- Moulded Case Circuit Breaker
MCCB's ranges from 32Amps even up to 1200Amps and more.
MCCB's breaking capacity starts from 15KA.
MCCB's occupies more space.
MCC's can't be used for small applications because of its
cost.
| Is This Answer Correct ? | 68 Yes | 12 No |
Answer / rvg.msceb
MCB- means is Miniature Circuit Breaker.
MCB having a bi-metallic strip thats senses the current
flow as the metal produces heat.
MCCB- means Moulded Case Circuit Breaker
MCCB 's are useful for high current applications,where bi-
metalic strip is not useful for sensing current through
heat. Its having a sensing circuit which senses current
throgh a group of resistances, and the calibration is very
necessary in such systems. beyond some specified value of
current, arc quenching medium to be incorporated. so
preferably MCCB rating should be less than say 600 Amps.
( if u have any comment pls write to
rvg.msceb@googlemail.com)
| Is This Answer Correct ? | 20 Yes | 12 No |
Answer / venkatesan.j
1. MCB stands for Miniature Circuit Breaker and MCCB stands
for Moulded Case Circuit Breaker.
2. MCB cannot be tripped from remote,whereas MCCB can be
tripped from remote as it has shunt trip ciol inbuilt in
it .
3. MCB has a fixed current setting whereas MCCB as range
through whitch it can be opreated.
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / j.s. patel
MCB- Miniature circuit breaker
> Low breaking capacity i.e. 9KA only.
> Low rating capacity i.e.available up to 63A only.
> Available in fixed range.
> Available in single pole.
MCCB- Moulded case circuit breaker
> Wide breaking capacity i.e. More than 85KA
> Available in wide range i.e. up to 1200A
> Adjustable range
> Not available in single pole
> Available with adjustable GF & short ckt. protection.
| Is This Answer Correct ? | 9 Yes | 8 No |
Answer / wasantha gamage
MCB- miniature Circite Braker minimum braking capacty is 6kA
MCCB- Molded case circuit Braker minimum braking capacty 1s 16kA
| Is This Answer Correct ? | 1 Yes | 6 No |
Answer / phanendra babu
MCB- MCB's are in rated capacity,these are not having any
range i.e if we take a 10A mcb,it will operate beyond that
only and these are open type(i.e not having any asing or en
closer.
MCCB-MCCB means moulded case circuit breakers,which is
having current range setting capability like relays. if mccb
is of range from 200A,we can set the operating range in b/w
min and max.
| Is This Answer Correct ? | 4 Yes | 10 No |
DG SET BLOCK DIGRAM
in india ac frequency is 50hz, but in foreign countries it is 60hz,whwt is the reason
which type of insulation are used on 132kv transmission line
how can we connect a distance relay to CT core that is for backup protection or metering?
What is mean by CT Saturate? how do we calculate?
What is an ac motor?
how much percentage set in transformer diffrencial relay
Three set (each phase contain 2 cable of 400 mmsq CU XLPE AWA) of single core cables are connected to 11 KV motor of 14 MW & the switch gear supplay is taken from 11kv feeder & this supplay taken from 275 KV substation. Problem is one pair cable(L3- 2 cable ) getting very hot & gland melted and damaged in switch gear side. the other two cable haven't any more hot(ambient temp only & L3 haveing 95- 100 Degree C. The same problem happened in 275 KV substation switch gear side also where the supply taken for 11 kv switch gear. But here L2 phese cable had problem. Why it is happening like this?. The cable having temperature different at different location from gland side inthe case of 11KV feeder of 275 kv substation. why ?
hi this is hema can anyone mail me previous years questions for the APPSC-A.E.E (in electrical stream.) ......thank u.
what is corona
what is earth-fault?when it occurs? to check where it occurs what type of test should we do?
how LVDT works?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)