Three set (each phase contain 2 cable of 400 mmsq CU XLPE
AWA) of single core cables are connected to 11 KV motor of
14 MW & the switch gear supplay is taken from 11kv feeder &
this supplay taken from 275 KV substation. Problem is one
pair cable(L3- 2 cable ) getting very hot & gland melted
and damaged in switch gear side. the other two cable
haven't any more hot(ambient temp only & L3 haveing 95- 100
Degree C. The same problem happened in 275 KV substation
switch gear side also where the supply taken for 11 kv
switch gear. But here L2 phese cable had problem. Why it is
happening like this?. The cable having temperature
different at different location from gland side inthe case
of 11KV feeder of 275 kv substation. why ?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
This happens whenever there is a loose connection or under -
sized lugs are used.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kaviraj
Get a thermal imager or camera, you will see the loose
connection very easily. I also bet it's a loose connection.
Else one of the cable cores has been broken. Check for sharp
bendings on cable. Copper braids still connected/earthed
properly?
| Is This Answer Correct ? | 0 Yes | 0 No |
what is mean by restructuring power system?
What is the major differences between RCCB & ELCB? If we use ELCB of less sensitivity why does it trip often and can we control it from tripping?
why generator one end side star neutral point given? if this point not given what happen?
The power dissipated by a resistor of 10ohm when a current of 2A passes through it is:(a) 0.4W(b) 20W(c) 40W(d) 200W
advantage,disadvantage,aplication of sensorless direct torque control of induction motor
In my project i am layout cables under the Maintainance bay /Maintainance yard in the TG Building. Whether in this route i can lay the H.T.Cables??? i am taking all H.T cables from the H.T Transformer to the TG Building..
What is sunrise meeting ?
why transformer rating is always in KVA
difference between brush less & brush excitation in a generator?
how to interlock 2 incomer,1 buscoupler MCCB,like we interlock an ACB... pls answer this question and if possible send me the ckt diagram..
what is the difference between circular wdg & ractangular wdg?
What is a parabolic signal?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)