Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


If connected load of Asphalt plant is 375Kw. What suitable
KVA DG set is required. What is calculation formula. what
extra load have to consider. in what efficiency it will
work.

Answers were Sorted based on User's Feedback



If connected load of Asphalt plant is 375Kw. What suitable KVA DG set is required. What is calcula..

Answer / ramesh kalsaria

calculation Formula=cos(phi)=kw/kva

Is This Answer Correct ?    28 Yes 4 No

If connected load of Asphalt plant is 375Kw. What suitable KVA DG set is required. What is calcula..

Answer / sukhvinder

connected load=375kw
kva=kw/cos phi
kva=375kw/.8
=468.75

extra load= 20% (assume) i.e 468*20%= 93.6

total 468.75+93.6=543.68 kva say 550kva

eff. 375/550*pf (0.8)*100=85%.

Is This Answer Correct ?    25 Yes 2 No

If connected load of Asphalt plant is 375Kw. What suitable KVA DG set is required. What is calcula..

Answer / munish saini

KW=KVA*PF
PF=.8
KW=375
KVA=KW/PF,=375/.8=468.75KVA

20 Percent required more as eppiciency Factor
so required dg should be=562.5 KVA

Is This Answer Correct ?    4 Yes 1 No

If connected load of Asphalt plant is 375Kw. What suitable KVA DG set is required. What is calcula..

Answer / virendra joshi

Dear friends,


Total Connected Load = 375 KW
KVA required @0.8 PF = 375 /0.8 = 468
Taking a 0.8 as a Demand Factor = 468 *0.8=375 KVA
Considering running of D.G set on 80% load = 3750.8=468 KVA
Considering 20% load for future expansion = 468 + 20%(93KVA)
Total KVA of D.G set = 561 KVA

you can go with 600 KVA D.G set .

Is This Answer Correct ?    2 Yes 0 No

If connected load of Asphalt plant is 375Kw. What suitable KVA DG set is required. What is calcula..

Answer / srinivas

if the connected load of plant is 375kw. but any time all
the load may not be there. if peak load may be 300kw at any
instant so KVA rating of DG=KW/cos(phi) so you can take
300/0.9= 333.33 so you can take 350KVA Dg you can go for.

Is This Answer Correct ?    2 Yes 3 No

If connected load of Asphalt plant is 375Kw. What suitable KVA DG set is required. What is calcula..

Answer / syed.yaseen

dear friends,

Given kw = 375
suitable kva = 375/.8 =468.75
Future extra load consider = 20% ie.. 93.75kva
total kva = 468.75 + 93.75 = 562.5
as per company designed capacity preferred is 625kva dg set

Is This Answer Correct ?    1 Yes 2 No

If connected load of Asphalt plant is 375Kw. What suitable KVA DG set is required. What is calcula..

Answer / vikash gupta

calculation formula:-kva rating=kw rating/cos phi

connected load=375w
kva=kw/cos phi
kva=375w/.8
=468.75w (ans)

extra load=(468.75-375)w
=93.75watts(ans)

efficiency =375*100/468.75
=80%

Is This Answer Correct ?    6 Yes 14 No

If connected load of Asphalt plant is 375Kw. What suitable KVA DG set is required. What is calcula..

Answer / sam

calculation formula is KVA= KW*Pf(cos phi)

KVA= 375*.9
KVA=337 so DG set will be more than 20% of rated KVA

Is This Answer Correct ?    21 Yes 34 No

Post New Answer

More Electrical Engineering Interview Questions

What is AVR in Generators and How is it working.

4 Answers  


Why use in ht motore

0 Answers   ACB Group,


How are calculated the aluminium busbar cross section area?

2 Answers  


How does zener phenomenon differ from avalanche breakdown?

0 Answers  


what is die electric strnth of transformer ?

0 Answers  


what is the difference between bus-coupler and bus-riser

2 Answers  


What is the main function of fuse?

7 Answers  


why h parameter are called as hybrid parameter?

0 Answers  


I have tow 200 KVA UPS, both are in parallel mode.My question is that, both are running on battery when power fail, if one of them fail (Eg rectifire fails or some other reason), at thet time reverse power will come to faild ups if it comes then it will harm to failed ups or not? if not then how it protects to faied ups????????????????

1 Answers  


what parameters should we check to reduce the power bill

0 Answers  


what is the name for a meter/tester to measure the paint quality in electrical panel or wall?

1 Answers  


Why capacitor bank is not neccessery to switch on,pls answ me with formula

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)