I have tow 200 KVA UPS, both are in parallel mode.My
question is that, both are running on battery when power
fail, if one of them fail (Eg rectifire fails or some other
reason), at thet time reverse power will come to faild ups
if it comes then it will harm to failed ups or not? if not
then how it protects to faied ups????????????????
Answer / sathishkumar
hi you mean both the UPS in PRS(parallel redundancy systen)
mode.then u have to connect the battery back to each UPS
separately.untill unless we are using as single sourse we
should not connect the both possitive terminals of Battery
bank connection in a common bus bar.if any one UPS failed
and EB power also goes off the entire load will be shifted
to single UPS which is working good condition also the
Battery bank which belongs to that battery bank only
support to the load.
remember in PRS mode output only paraled not input sources
(AC mains and battery back up)
Is This Answer Correct ? | 2 Yes | 0 No |
what is the difference between oil surge relay and buchholz relay.
Why do we choose 33kV transmission for industrial purpose and 11Kv for township?
how much current will be drawn by 3 phase, 415v, 50 hz, 20 ton central ac
1.Defination of Graund earth and neutral 2.
If I want to use capacitor banks at HT (11 KV) side for maintaining power factor then which type of capacitor should I use? Plz give me the specification?? (I am using 1250 Kva transformer (11 KV/433V)).
is it possible to use a tranformer to regulate an unstable system voltage?
what sort of general awareness questions are asked in o.n.g.c entrance exam?????????????????
Technical specification of a wind farm
Why the earth cable have current 1A - 2A , it is safety for Electrical system or earth cable should be zero amps ? how to troubleshoot?
What is the difference between synchronous motor & asynchronous motor
hi all, can any one tell me a website or document on basic interview questions on plc for a fresh diploma candidate?
What is the equipment used to control the generator output?