if we convert watt into kva,which one formula use by us,pls
tell me?
Answers were Sorted based on User's Feedback
Answer / k.suresh
in 3 phase system,
kw = 1.732*v*I*pf
where kva = 1.732*v*I
from the above 2 formulas,we can convert watts to kva
| Is This Answer Correct ? | 15 Yes | 4 No |
Answer / jyotirmaya
For 3 Phase Supply
KVA = Watt/ (1.732 x p.f.x 1000)
For 1 Phase Supply
KVA = Watt/(p.f. x 1000)
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / ashish umrao
kw=v.i.cos*
kva=v.i.
cos*=kw/kva=kw/cos*=kva proved
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / nidhi
formula
V*I (Cos)=KW= (V*I*P.F.)
but KVA=V*I/1000
SO
KW=KVA* P.F.
where P.F.=Cos (angle between V&I)
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sheikmohammedilyas
IN three phase motor,
Power= square root 3 *v* i* cos teta
-------------------------------
1000
1.732 *V*I*cos teta
W = -------------------------------
1000
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / khaleel
cos*=KW/kva (from power triangle)
so kva=kw/cos*
| Is This Answer Correct ? | 0 Yes | 0 No |
how many wires need to be bring to the motor if its star delta starter
what is the use of earthing?
How to calculate incoming cable size for 33KV, 1MVA transformer.
how to select electronic timer(Star-Delta) setting for diff. rating motors
0 Answers Getrag Ford Transmissions,
WHAT IS THE MEANING CREEPAGE DISTANCE
what is the difference between LATCH and FLIP FLOP
How each of the following losses occur in d.c machines (i) copper (2)core (3) windage (4)friction please help me
what are clipper and clamper circuits?
For 7.5kw star delta starter how to calculate 1. Mccb rating 2. Contactor rating 3. Over load relay rating
How can we calculate D.C.Load current in terms of A.C. load current?
1.WHAT ARE TRANSMISSION LINE LOSSES DURING WINTER AND SUMMER SEASON? 2.WHAT ARE THE CAUSES/ 3.WHEN THE CORONA IS MORE?.,WHETHER WINTER OR SUMMER? 4. WHAT IS THE PERCENTAGE OF LOSSES IN TRANSMISSION LINE?
When One Phase PT Missing (voltage drop ) this time current is zero of This phase(PT Missing Phase) and current is Not Zero of other Phase but PF is always Low That Why
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)