How to calculate incoming cable size for 33KV, 1MVA transformer.
Answer / ak
calculate line current for transformer
I=1000000/(1.732 x 33000)
=17.50 Amps
based on the value of current select appropriate cross section area of particular gauge.
Is This Answer Correct ? | 6 Yes | 1 No |
If NO contact of relay gets supply from other sources or other part of circuit and at a time relay coil activates,then current will flow in which direction & will it cause to damage relay??
why they were using TRIAC instead relay in some controllers and what is the advantages.
what does work of electrical technician in industrial
active elements are those which are capable of
I want to put this query to SENIOR & EXPERIENCED ELECTRICAL ENGINEERS. 1)I want to know about the control circuit diagrams for control panels. I found it difficult to understand. Is there ant booklet through which we can learn the circuit diagrams? 2)I want to learn about conduiting, laying cables, preparing cable schedules and various techniques which is the part of building infrastucture(construction field). I don't have any experience in this area. I have experience in control panels only. that's why i am not getting any opening in building infrastucture (construction field).Can I get the job in this field as Trainee Engineer? How to enter this field? I need job in PUNE
what type of load we can give to motor shaft?
sir i used 3 hp of motor for spraying pump, other home light and other home items which size of allminium pvc wire ix used
how do i work out the Amps of a incommer if i am running 1 37 KW motor and a 0,75 KW motor and some solinoids
Which standard we are following earthing resistance test
how does high earth to neutral voltage affects electronic circuit?
if step down transformer step down the voltage,will current will also be proportional step up. If yes then how transformer handle such a large current?
what is load vs Torque curve & why it is used?