What happen if LV supply is fed to a HT motor?
Answers were Sorted based on User's Feedback
Answer / m.anand
if we connect an ht motor with LT supply the motor run
according the magntic field produced by them.and then also
the torque developed by the LT supply is much lesser than
the torque devloped the HT supply.for example if we pull a
load with 100% of energy is not equal when we pulling the
same load of 20% of energy
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / shubh
If LT supply is fed the motor will start with a slow speed
but slowly and surely it will reach the required spped
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mahesh meshram
If HT motor fed on LT supply, motor will run slowly and speed will increase with time. Initially motor will draw app. 1/3rd of the rated current and it will also reduce by 2-5 amp and will get steady.Motor such type of performance is expected only if it's bearing, rotor and other factors are good.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / atta
HT MOTOR WILL NOT RUN DUE TO LOWER MAGNETISING EFFECT
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / singaravelu
There is no problem on it's winding and it's torque and it's rpm will reduced and it will runs at a short duration minimum one hour continusously it will runs there is chases to coil burn.It will held to test the Motor and find it's housing problem.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ankur
As power taken by motor is VIcos@, so if less voltage will
be applied on the motor then in order to develop magnetic
field in the motor i.e in between rotor & stator, it will
take large current as compared to it rated current, result
in over heating of winding, excess losses, and finally
winding will burn out.
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / ramya sree
Hv windings are designed such that they have more number of
turns to get high voltage, also less thickness as it carries
less current.comparitively, Lv windings are designed such
that they have less turns and more thickness so that they
withstand high current. when such high current is passed
through hv winding, being thin it cannot withstand such high
current,due to heat developed, winding may burn.
| Is This Answer Correct ? | 0 Yes | 2 No |
if LT applied to HT motor then motor winding will burn out.
because motor current is inversely propotional to voltage.
i f applied less voltage the motor current will increase.
e.g.
1500 kw motor supply voltage 6.6 kV current 155 A.
if applied 415 V then current is around 2000A .
| Is This Answer Correct ? | 26 Yes | 63 No |
motor winding will fail under low voltage.
| Is This Answer Correct ? | 16 Yes | 58 No |
how to synchronize 4 nos. of diesel generator sets of different capacity (kva)?
What is the d/f b/w MCCB & MCB
how balanced in star delta connection ?
what is load despatching
diffrence between alternating and pulsating field?
How to calculate LT XLPE CABLE for 11 kv / 433 v , 1000 kva oil type transformer system?
dear sir, How i calculate the 2 phase welding transformer power or kva?? kindly tell me....
what is static switch where it can be use?
What is difference between Ac Voltmeter And Dc Voltmeter ????
Give two basic sprrd control scheme of DC shunt motor.
if we want ot select cable size with reference to load current it take than what is the formula and it is same for aluminium or copper?
how braking & making capacity of circuit breaker is calculated?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)