Answer / suresh
due to low voltage less magnitic fied to rotate the motor
when we must rotate initially. no torque developed.
testing purpose ht motors run on lt supply through dimmer.
| Is This Answer Correct ? | 82 Yes | 11 No |
Answer / ketan verma
HT motor will rotate at a low speed if 415 v power supply
is given to the terminals of an ht motor. This a a type of
test in which if the moisture is found in the motor then
the same can be evaporated by this method. Moreover, there
is a test called block rotor test in which we can block the
rotor shaft and give the 415 v power supply to terminals
and thus the heating will occur in the winding and thus the
IR value will improve. This has been practically testes by
us at lot of sites....
| Is This Answer Correct ? | 49 Yes | 1 No |
Answer / mangesh mane
as supply is lv, motor torque will became low if it will
lower than minimun torque required to just rotate the
motor then motor will not run or rotate otherwise it will
rotate at lower speed than rated speed & motor current will
remain less than 6 times of its rated current
| Is This Answer Correct ? | 34 Yes | 7 No |
Answer / anand ahuja
If 415V 3-ph 50Hz power supply is connected to a motor which
is rated, say, 3.3kV or 6.6kV or 11kV, the motor will not
start at all as it will not develop sufficient magnetic
field and there it will not develop sufficient torque.
Basically, the number of turns in a HT motor are high
compared to the no. of turns in an LT motor. When LT
voltage is applied to HT motor, the voltage drop per turn or
the emf per turn is very low and thereby it does not develop
sufficient magnetic field.
In case of a star-delta start of normal LT induction motor,
the voltage applied (or potential applied) to the windings
is less in star connection than that in delta connection.
In case of LT motors, the current drawn is high on low
voltage being applied to it when it is within a certain
range. That is a 415V motor is connected to 380V or 320V
supply.
Whereas, applying 415V to a 3,300V or 6,600V or 11,000V
motor is similar to applying voltage as low as 20V to 40V to
415V motor.
| Is This Answer Correct ? | 31 Yes | 8 No |
Answer / vinodkumar
motor will not run or will run at low speed
| Is This Answer Correct ? | 15 Yes | 4 No |
Answer / balkishan gothwal
We can give 10% of HT voltage to LT motors for testing
without no nolad.Some time you may push to get in rotation
once if it picks speed it will be rotating with the same
speed as HT voltage provided the frequency will be
same.Because the speed depends on frequency not on voltage.
this is used for healthiness of motor by applying LT
voltage to HT motors.
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / a v subba rao
We can connect HT motor with LT supply in no load with out
any problem for site testing. Only thing motor will not
start due it will not devalop sufficient torque,but if we
rotate the shaft at the starting motor will start rotating
at lower speed first and it will slowly increse to up to
rated speed if we can not remove the supply. This test has
to be done only idle motor.
| Is This Answer Correct ? | 12 Yes | 6 No |
Answer / sameer vijayakar
motor will pick up the full speed slowl as the motor runs
on low torque and the inertia helps in pcking up speed as
the torque is consistently applied.
| Is This Answer Correct ? | 4 Yes | 0 No |
How we can convert H.P into KW or Vice versa
transformer spections :: input voltage 0-110-230v; output volage 0-10-12-14v; amp=3A using CRNO CORE, capcaity=50VA primary turns = ? ; secondry turns =?
Why RCD trips on connecting to one Socket but not trips one other circuit on same RCD.
What should be the percentage increase in length of the dead end clamp for bus bar conductor (Hawthorn) after hydraulic pressing and what should be the applied pressure?
Why in 6 KV XLPE cable termination kit used and why not in 380 V xlpe cable same is not used
what will happen if we give a dc supply to a transformer.?
What type of bulb used in small size cross symbol boder and original flame type(Deepam)?
what is the mazor difference between the induction transformer and synchonous motor?what is the similarity between them?
Difference between Profibus DP/PA?what does it stand for and how is it use in process?
Why in USA supply voltage parameters(230V,60Hz)are different,is there any advantage please brief.
what type of loads are inductive load & resistive load ?how they different between each other ?
1. which type of transformer connection is preferred in case of power supply transformers? (A) Star/Star (B) Delta/Delta (C) Star/Delta (D) Zig Zag/Star 2. In a power transformer usuall which winding is closer to the core? (A) Primary winding (B) Secondary winding (C) Low Voltage winding (D) High Voltage winding 3. The power factor of a purely inductive load is (A) Zero (B) Lagging (C) Leading (D) Unity.
9 Answers CECRI_Central_Electrical_Research_Institute,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)