Answer / bhupinder
In the same way as we have to synchronise the same capacity
generators. Capacity of source doesnt matter , the only
thing is F , V and phase of all the sources should be same
at the time of synchronising.
Is This Answer Correct ? | 58 Yes | 7 No |
Answer / srinivasan j
First we satisfy the three Conditions
1.Frequency
2.Voltage
3.Phase Sequence
Capacity is not the matter because we synchronizing 4 engines
at different capacity 1000KVA - 2No's
1100KVA, 1150KVA.
Is This Answer Correct ? | 17 Yes | 1 No |
First of all it is possible to have different size of
generators synchronized. If the condutions of voltage
frequency and phase angle is correct. The load sharing must
be set for a percentage load. This means all set will have
the same load (example 60% of max load on all sets).
Issues can be where the load sharing is not set correctly
or where the governor response is too different. This can
cause hunting of the load from one set to the others.
Another inportant consideration is the wave form. If it is
different high current can flow through the neutral. If the
alternators are made by the same company this is not an
issue.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / sudhanva madhukar mahamuni
Dear All,
Kindly note that we cant / can synchronise DG sets of
different sizes. There are some major conditions which are
not allow to synch. differrent sizes of dg sets.
assume that 500kVA and 250kVA DG Set we have to syn.
if we loaded 80% on 500kva dg set + 50kva, then 250 will
start up and syn. with 500 kva but kindly note that it will
not share only 50 kva or both will not share the load
equally. and when load will get decrease then due to hunting
effect bigger size will share more load than lower one and
cascade tripping will take place.
Is This Answer Correct ? | 9 Yes | 7 No |
Answer / pandiyarajan
We can synchronize if voltage, frequency & phase angle match.
Loading on different size DG set depend on the capacity & impedance value.
Is This Answer Correct ? | 4 Yes | 6 No |
Answer / chat lang
yes im agree all your answer because we experience this
kind of problem we use 3nos of 500 and 1nos 1150kva this is
synchonized connection, then the 1150kva genset is shutdown
and he dont want to accept load sharing yes he start for
1hr but then shutdown he dont want to have load sharing in
other genset and on the ((DSE scada module)) telling or
indicating is no communication on main unit, then we
disconnect that ((1150kva genset. the spec of genset is
same like the 3nos 500kva pf 0.8 rpm 1500 HZ 50)) so what
was the posible cause of this problem,
Is This Answer Correct ? | 1 Yes | 3 No |
why rating of transformer is in kva instead of kw?
Can the same motor be operated in both direction ?
WHAT IS MEANING OF VECTOR GROUP FOR TRANSFORMER
Why motor is not calculated in kva, whereas transormers are calculated in kva
Why Lightning arrester used? Can we use piece of iron as a core material of transformer, if No, why? In CRGOSS material what is meaning of cold rolled grain oriented? Why Impegrenation of Transformer is done? Properties of Insulator? what is phase angle? Testing of transformers (Routine & Monthly)?
why the undervoltage relay's interlock is used in earthswitch closing operation of the 400kV line scheme?
Necessity of transformer earthing
What is reactive power?
diff. between star, delta connection?
Why we use 4-20 mA Analog signal for the PLC input? Why not 0-20 mA? Why not 5-25 mA?
WHY CBCT USE ONLY IN Y PHASE NOT OTHER PHASES
pls tell us AC plant are how do work and parts name with picture