I have installed capacitor bank at secondary transformer.
cos phi is increase. but on load (far from transormer), it
still poor. Can anybody explain it??
Answers were Sorted based on User's Feedback
Answer / jinu
capacitor bank will improve the power factor towards the
supply side only. ie if you are measuring the power factor
before the capacitor bank it will show the improved power
factor. But the same time when you measure it after the
bank it will show you the load power factor not the
improved power factor.
Is This Answer Correct ? | 19 Yes | 0 No |
Answer / heamkumar
Capacitor Bank is used to improve the Power Factor.
As you said, Pf will increase only in the incomer side.
Because you have connected the capacitor bank in the
secondary side near the incomer. So if you need to improve
the pf near load, you need to place the capacitor bank near
the load, but according to the load. So if you put the
capapcitor banks near the load side, power factor will
improve not only in the load side, but also in the incomer
side.
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / joseph
Since the reactive power compensation (capacitor) is
provided on the LT side of the transformer, the
compensation will take place upstream from the point of
connection. Between the point of connection and the Load,
the reactive power still remains uncompensated. Hence, in
case the loads are not very small and vastly distributed in
the network, it is better to provide reactive compensation
at the load end itself. The only disadvantage is that
there should be arrangement to switch off these capacitors
when loads are not ON, otherwise, the capacitors themselves
would act as loads!
Is This Answer Correct ? | 3 Yes | 1 No |
first a fall caluclate the reactive power. after that
according to reactive power caluclate requied capacitor to
be arrange then u will increase power factor.
kVAr = KW {tan(cos^-1 Phi e) - tan(Cos^-1 Phi d)}
Where - Phi e = existing Power Factor.
Phi d = Desired Power Factor.
Is This Answer Correct ? | 2 Yes | 4 No |
Answer / niranajn
Because the capacitor abnk provides the ractive power
needed near a transformer but it cant provide the
kvar required by the line so the power factor is still
low
Is This Answer Correct ? | 1 Yes | 4 No |
what is the highest transmission voltage in india???
49 Answers Bhel, EIPL, Engineering, Jindal,
using n1*n2 which type transformer is made; where n1 is primary turn and n2 is secondery turn
if an alternator or turbine using fuel to produce ele energy and we didn't connect load to the ends then where was gone the ele energy
Show the schematic arrangement of diesel power station layout and give its principle of operation.
what is relay what is protection & contact multiplying relays where it is used function in brief
what kn of disc is used in 33kv,132kv,220kv,400kv,800kv transmission line
what is diff btw electric,magnetic & eletromagnetic field
why capacitors cant used in genset to maintain power factor..??
Wtat is vaccum currcuit breaker.define with cause of used.and where be use it Devise .
iam working as a electrical engineer. i want to know about any license or certificates regarding my field. for my carrier and ti improve the knoweledge.,,, how we get that..and what procedures......... pls help me
What is the basic working principle of Tri vector meter?
what is meant by vector group of a transformer? How can it be derived?