1KVA transformer of different frequencies of
50hz,100hz,500hz&1000hz. which one of these transformer has
big size? Give reason
Answers were Sorted based on User's Feedback
Answer / kishore
X(1 KVA) 50 HZ n Y(1 KVA ) 500 HZ
E = 4.44 f * FLUX * N
that is emf durectly proportional to flux which is f*B*A
B- flux density n A= area of c/s of transformer
as KVA reting of both are same n hence
X (f*B*A) = Y (f*B*A)
as frequency of X is smaller than Y so area of c/s of X
must be larger
hence 50 HZ transformer is largest and so on
kishoresahoo@ymail.com
Is This Answer Correct ? | 39 Yes | 8 No |
Answer / bhanu(secure meters ltd.)
due to some mechanical constraints, generally transformer
size is inversely proportional to the operating frequency.
thus 50 hz, transformer will have max.size.
Is This Answer Correct ? | 18 Yes | 3 No |
Answer / asutosh
with increase in frequency the size decreases so the 50 hz
will have big size
for better understanding refer high frequency transformers
Is This Answer Correct ? | 15 Yes | 3 No |
Answer / ambi
this is a short cut method based on analysis..
generally power transformers use lower frequncy(50hz) and
we know in electronic ckts like oscillators producing very
high frqs in range of KHz we use only SMALL trfrs than pwr
trfrs.... so on analysing we can conclude tat higher
frquency transformers have less volume...
NOTE: this is only shrt cut mthd, actual reason depends on
the FORMULA only for determining the size
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / chankey garg
while increasing freq width of stamping decreases so 50hz
having bigest size
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / mohd shahid
bhai kishore see here we r talking about same KVA rating
not same KV rating.
here you r equting the KV rating(ie by equating the induced
emfs)
there is a diff between kv and kva hence kindly refer again
to your solution which acco. to me is not correct
Is This Answer Correct ? | 8 Yes | 3 No |
Answer / rahul
The EMF of a transformer at a given flux density increases
with frequency.By operating at higher frequencies,
transformers can be physically more compact because a given
core is able to transfer more power without reaching
saturation and fewer turns are needed to achieve the same
impedance.
So, 50Hz transformer will be the bigger one.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / r k alaria
The impedance of the transformer is greater for higher frequencies (as X=wL). So for constant voltage to keep same current rating (because for constant kVA)we have to reduce the inductance of the winding. And to reduce the inductance we have to reduce the no. of turns in the windings of the transformer. By reducing the no. of turns the size of the transformer will be reduced for higher frequencies.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / engr. ziaul ashraf shafi
Mohd Shahid,
From the eqn V/F= flux, you wrote that "increasing the
frequency will cause the flux increasing. HOW ??
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / ganesh.m
Consider the primary of a transformer is operating at 230V,
50Hz. Consider the the secondary of the same transformer
generates 12V, 50Hz. What will happen to the secodnary
voltage, if the primary is fed with 230V,1KHZ supply?
Is This Answer Correct ? | 5 Yes | 4 No |
WHY ARMAD USE IN CABLE
What is an order of a system.
cable selection formulas for electrical load.
I HAVE 2 nO'S OF SYSTEMS, HOW MUCH UPS CAPACITY REQUIRED ALONG WITH 400WATTS ANOTHER LOAD? PLEASE GIVE THE FORMULA?
For single phase(phase to neutral) having potential difference 230.in three phase(phase to phase)we have 440V HOW...?
operation of diesel generator
draw the full wave and half wave circuit of 3 phase system and inverter circuit used in ups
what is the use of capacitor in online ups?
ASTM D 3455 - Standard Test Methods for Compatibility of Construction Material with Electrical Insulating Oil of Petroleum Origin has been used for Testing Transformer Oils with a product placed in it. Aged Control Oil has a Power Factor of 0.032% at 100°C. Aged Oil with a Test component has a Power Factor of 0.093% at 100°. Is this increase acceptable? If not why? How much increase is acceptable?
What is CBCT ? Why & Where it is used?
what is the function of choke and starter in a tube light??
how to deside the capacity of chock for drive?