1KVA transformer of different frequencies of
50hz,100hz,500hz&1000hz. which one of these transformer has
big size? Give reason
Answer Posted / kishore
X(1 KVA) 50 HZ n Y(1 KVA ) 500 HZ
E = 4.44 f * FLUX * N
that is emf durectly proportional to flux which is f*B*A
B- flux density n A= area of c/s of transformer
as KVA reting of both are same n hence
X (f*B*A) = Y (f*B*A)
as frequency of X is smaller than Y so area of c/s of X
must be larger
hence 50 HZ transformer is largest and so on
kishoresahoo@ymail.com
Is This Answer Correct ? | 39 Yes | 8 No |
Post New Answer View All Answers
For overhead protection we use which transformer?
Give some example of fault limiting devices?
Can you explain about pole discrepancy scheme
why ten delta testing is carried out on power transformer
why do we lay up the core of a cable?
How to check 11000/1.732 to 110/1.732 Potentila transformer (PT)?
salam,hi, i need to know what the spesification of 300amp msb...
What is the Temperature to be set in Thermostat provided in Marshalling box of the Transformer / Motor.
If one tertiary phase i.e. R,Y or B is earthed of a loaded type tertiary delta connected (Without load)of a power auto transformer, what is its advantage/disadvantage?
What range of speed can you get with the armature control method of speed control of d.c. Shunt motor?
Do closed loop systems require manual input?
when ID fan will immediately stop through VFD what exactly cause and problem the ID fan
What are the causes of having an rmu explode after installation? And how do u treat the bushings of an rmu?
Why armature rheostat is kept in maximum position?
What will be the voltage regulation of a full load and 0.80 power factor lagging load transformer when a two winding single phase transformer has a voltage regulation of 4.5% at full load and unity power factor?