cable selection formulas for electrical load.
Answer / engineered
Factors for selection of cable
1.Rated current
2.voltage drop across cable
3.derating factor based on temprature,no. of cables laid
through same path influencing each other
4. Type of laying method:- like air, ground, duct, tray,
raceway
5. type of conductor required.
6. type of insulation, like PVC, XLPE, FRLS based on site
condition
| Is This Answer Correct ? | 3 Yes | 0 No |
wat is the need of capacitor on aceiling fan?
What is the Levels of High Voltage, Medium Voltage & Low Voltage?
how we have to calculate the short circuit current for 33/11kv 2mva, 7.5% Z, Transformer primary side breaker and secondary side breaker short circuit current for both sides?.
How to select the rating of a CT used for REF protection. The rating can be of equal rating of Phase current or neutral current rating
what is work of CTPT in 33/11kv Substation
what is doubling factor in making current of a breaker?
solar inverters was not connected to the nuteral link .this nutwral possible to any other systems
What will be the full load current of 60KVA UPS. Suggest for this formula.
Why do u join toreent power ?
I have current, kva How can calculate kv?
will there be any problem by recovering slip from single phase induction motors?
will we get shock from dc?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)