Answer / dhanraj
For 33 Kv cable DC hi pot test can be done like (2*E+1)1.414
here E=Voltage , 1.414 is the root 2 value.
Now (2*33+1)=67Kv
Then 67*1.414=94.738 Kv this is 100% of cable test.
In manufacturing factory they will test up to 80% of the voltage in that 100% (94.73*0.8)=75.79 Kv.
But in consumer side they will test up to 80% of voltage that injected in the factory voltage (75.79*0.8)=60.64 Kv.
Now 60.64 Kv is apply for 3 mins maximum.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / michael aliganga
CABLE FACTORY AC TEST VOLTAGE =2E+1kV= 2X35+1= 71kV
DC HIPOT TEST:
CABLE INSTALLATION TEST DURING AND AFTER = ET= EF X 1.8 X 0.8
ET = 71 X 1.8 X 0.8 = 102kV, ICEA DC FIELD TEST VOLTAGE
(ICEA S-97-682) IS 100 kV FOR 35 KV SHIELDED POWER CABLE.
EF=CABLE MANUFACTURERS RECOMMENDED FACTORY AC TEST VOLTAGE
IF NOT AVAIABLE USE 2E+1KV
1.8 AC TO DC CONVERSION FACTOR (QUITE COMMON)
0.8 CONVERSION FACTOR FOR DERATING FROM FACTORY TESTING TO
ACCEPTANCE TESTING.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / manohar
Hipot test conduct for 33kV cable is 1.5 times of rating
voltage in DC(49kV approx will be apply for 1 minute.)
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / martin thomas
Iec code
Ac= (2 x e) 1
Dc={(2 x e) 1} x 1.414
1.414=sqrt (2)
E= rated voltage
Aramco std
Dc =4 x u
U= phase voltage
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jagan
33kV cable hipot Test
33*2+1=67
67/√3=38.68 for single cable
38.68*√2=57.8 for diode dc convert RMS
57.8*0.8=46.3 for dielectric % reduce by year
Finally apply new cable 46.3KV /phase
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a.shiva krishna
AC Hipot test voltage = Nominal input voltage * 2 + 1000
DC Hipot test voltage = AC Hipot test voltage * 1.414
for 33kv
ac hipot v/g = 33000*2+1000 = 67kv
dc hipot v/g = 67000 * 1.414 = 95kv
| Is This Answer Correct ? | 16 Yes | 25 No |
Answer / raveendra
(2E+1)=67 kV FOR AC HIPOT ( 1 minute test)
67*1.7 = 113.9 DC HIPOT ( i minute test)
for aged cables generally we will apply 65% of the above
| Is This Answer Correct ? | 24 Yes | 37 No |
I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel with 4000A Breaker.Already I have 2500A load.Can I connect this load directly to the Busbar since I have PROTECTION IN MY MDP Panel ?
we have a rewind motor of 2Hp,2800Rpm, 220Volt AC. how can we choose the running capacitor for this motor, any formula for that?
what is brushless generator.How does work it..??
What is the difference between LT & HT Cable
what is mean by ideal infinite bus? why it is required to consider in fault short circuit calculations?
Pls anyone explain me the basics of wiring a house?
how a flip flop can be used as a latch?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
WHAT IS THE MEANING OF 'UPF'&'LPF'.... HOW CAN WE DEFINE IT? WHAT IS THE VALUE/RANGE OF EARTH WIRE RESISTANCE USED PARTICULARLY IN HOME....
Why choke coil is connected in series with starter in tubelight??why starter is connected in parallel to tubelight??
does magnetic interlocking take place in an induction motor ?
why is efficiency of transformer more than that of other rotating machines?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)