I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel
with 4000A Breaker.Already I have 2500A load.Can I connect
this load directly to the Busbar since I have PROTECTION IN
MY MDP Panel ?
Answers were Sorted based on User's Feedback
Answer / jagadisha.n bmsit
ya we can..
Actual rating of the motor is 4000A and it was carrying
2500A load since if we connect 500A tio same busbar it
becomes 3000A so it can handled both the load but the prob
is if fault occured in 1 line both the line will trip..
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / santosh bangar
no , because it will trip 2500 A load if fault occur at MDP
it is possible if MDP have it's breaker to clear fault.
then you can connect to MCC bus
Is This Answer Correct ? | 0 Yes | 0 No |
Dear friend.
Mathamatically it looks possible but bofore making this
arrangment the other factor which you need to consider.
1. The Rating of a transformer.
2. the Ir seeting of a Breaker.
3. Total contract demand if you are using local electricity
board power.
4. change in OT & WT setting.
by checking all the above peramiters you can go ahead.
Is This Answer Correct ? | 0 Yes | 1 No |
is there any lightning by passer is arranged in ship like buildings?
Why is the uniform distribution of the capacitor discs in a suspension type insulators essential , what can u do to improve the string efficiency ?
A 230V, 60W bulb when connected to 230v supply what current and power will consume, if same bulb is connected to 200v what purrent and power will consume?
Can u tell me about HVDC transmission?
is it possible for different brand of H.V transformers to run or operate in parallel to each other? if so how much disturbance can this affact the H.V bus bar?
why we use perllel conection system in the wiring?
opkinson's test
how to setting voltage RTCC panel
What are the protection used for alternator,transformers.
who can measure the size of power cable?
In DC current-excitation to transformer, why it sucks more current? Eventhough there is no power transfer between primary and secondary? R is very low so it should suck less current only na thn y its current increases?
which type of insulation are used on 132kv transmission line