Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel
with 4000A Breaker.Already I have 2500A load.Can I connect
this load directly to the Busbar since I have PROTECTION IN
MY MDP Panel ?

Answers were Sorted based on User's Feedback



I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel with 4000A Breaker.Already I have 2500..

Answer / jagadisha.n bmsit

ya we can..

Actual rating of the motor is 4000A and it was carrying
2500A load since if we connect 500A tio same busbar it
becomes 3000A so it can handled both the load but the prob
is if fault occured in 1 line both the line will trip..

Is This Answer Correct ?    7 Yes 0 No

I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel with 4000A Breaker.Already I have 2500..

Answer / guest

yes you can

Is This Answer Correct ?    3 Yes 0 No

I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel with 4000A Breaker.Already I have 2500..

Answer / santosh bangar

no , because it will trip 2500 A load if fault occur at MDP

it is possible if MDP have it's breaker to clear fault.
then you can connect to MCC bus

Is This Answer Correct ?    0 Yes 0 No

I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel with 4000A Breaker.Already I have 2500..

Answer / virendra joshi

Dear friend.

Mathamatically it looks possible but bofore making this
arrangment the other factor which you need to consider.

1. The Rating of a transformer.
2. the Ir seeting of a Breaker.
3. Total contract demand if you are using local electricity
board power.
4. change in OT & WT setting.


by checking all the above peramiters you can go ahead.

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

Three set (each phase contain 2 cable of 400 mmsq CU XLPE AWA) of single core cables are connected to 11 KV motor of 14 MW & the switch gear supplay is taken from 11kv feeder & this supplay taken from 275 KV substation. Problem is one pair cable(L3- 2 cable ) getting very hot & gland melted and damaged in switch gear side. the other two cable haven't any more hot(ambient temp only & L3 haveing 95- 100 Degree C. The same problem happened in 275 KV substation switch gear side also where the supply taken for 11 kv switch gear. But here L2 phese cable had problem. Why it is happening like this?. The cable having temperature different at different location from gland side inthe case of 11KV feeder of 275 kv substation. why ?

2 Answers  


Pl.brief me about Electrical power distribution system from Main generating station to Industry.What is the use of in between station.

0 Answers   ARDE,


AIR GAP IS TERMED AS USEFUL. WHY?

5 Answers  


definition of transformer

10 Answers  


How to select the releases for MCCB ?

1 Answers  


what are the points to be consider for MCB(miniature circuit breaker selection?

3 Answers  


WHY THE FREQUENCY IS 50 HZ IN INDIA.CAN WE USE SOME OTHER FREQUENCY.IF SO WHAT IS THE RANGE AND WHAT WILL BE THE EFFECT IN PRESENT POWER SYSTEM IF WE CHANGE THE FREQUENCY AS YOU SUGGEST ?

32 Answers   L&T, MCL,


LT cable fault chaecking equipment and to find out the distance at what distence it failure . Name and where it is available?

0 Answers   Himatsingka Seide Ltd,


Why does the rotor rotate?

0 Answers   Elin, OPTCL,


whate is the meaning of balance/unbalance,in stabilizers type

0 Answers   TCS,


What is the size of a 60 watt and 80 watt tubelight?

0 Answers  


Why thwe Direction of Rotation of a TABLE Fan & CEILING Fan are different?

8 Answers   Wipro,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)