What is the Difference Between MCCB & ACB & VCB
Answers were Sorted based on User's Feedback
Answer / minal
Mccb is moulded case circuit breaker.
ACB is air circuit breaker.
VCB is vacuum circuit breaker.
Is This Answer Correct ? | 1190 Yes | 190 No |
Answer / shahnawaz
MCCB,VCB,ACB all are of different type with same
functioning.
all of them are used to isolate the power or to trip the
power at the time of fault in line and thus save the
circuit from further damage and isolate unheathy part from
healthy one.
if the circuit if of low rating we can go ahead with MCCB
but for high rating circuit we go for costlier CB that is
ACB/VCB because they are more reliable and have long life.
Is This Answer Correct ? | 940 Yes | 121 No |
Answer / senthil kumar
MCCB,ACB,VCB all the three are protective devices only.
They are used to isolate the system which is connected
below them at fault conditions. Eg, Overload, Short
circuit,Earth fault.
Depending upon the operating voltages and level of
protection(Fault Level) needed for the system ,these three
protection device are selected.
For Eg: If the operating voltage are below 1100V, depend
upon the fault level we can use MCCB or ACB.
Simillarly if operating voltage are more than 1100V,VCB are
used.
Is This Answer Correct ? | 361 Yes | 69 No |
MCCB - Thermomagnetic operaton-For large surges in ct- In
distribution boards-bimetallic strip responding to less
extreme but longer_term over_current conditions-applicable
for
low voltages.
ACB - low volt power cb-trip characteristics r
adjustable-air s the arc quenching medium-applicable upto 440V.
VCB - medium volt power cb-trip char. adjustable-mechanical
sys. used for trip & open-Vaccuum s the arc quenching
medium-applicable upto 36kV.
Is This Answer Correct ? | 333 Yes | 97 No |
Answer / kola raju
MCCB: means moulded case circuit breaker which use ark
quenching device as AIR which is used upto 500 Amps only
ACB:air circuit breaker which use quenching device as air
and used upto 3000 Amps at 415 volts
VCB:vaccum circuit breaker which use ark quenching device
as a vaccum and used for 415 volts.6.6 KV,11 KV,33 KV,132
KV,220 KV also.
Is This Answer Correct ? | 244 Yes | 85 No |
Answer / balaji
MCCB which is nothing but moulded case circuit breaker.
ACB is nothing but Air circuit breaker and Vcb is Vaccum
circuit breaker..The main difference between last two thing
is the arc quenching medium.ACB is air and VCB is
vaccum.these two things are used for power tr and
distribution and MCB,MCCBs are used in small rating
machines also...
Is This Answer Correct ? | 162 Yes | 51 No |
Answer / sendô
VCBs are used primarily for medium voltage circuits (11kV
in UK), due to their better arc quenching abilities (these
high voltages in ACBs or MCCBs would cause an arc between
the terminals and render the breaker useless).
The fundamental differences between ACBs and MCCBs are.
1. MCCBs cost far less than ACBs
2. MCCBs are better at lower interrupt currents (below
630/800A), ACBs are better at higher currents (800A and
above)
3. ACBs are a lot bigger and take up large sections of
panel that you might be able to fit 3 or 4 smaller MCCBs
into.
4. The main advantage is ACBs perform better under high
current short circuits, and will normally withstand for
long enough to allow a downstream device to open and clear
the fault, thus localising the short circuit trip.
5. ACBs are more easily serviced (particularly withdrawable
type).
Is This Answer Correct ? | 104 Yes | 15 No |
Answer / harikishan chaturvedi
MCCB-MOULDED CKT BREAKER USED FOR LT SIDE
ACB-AIR CKT BREAKER USED FOR LT SIDE
VCB-VACCUME CKT BREAKER USED FOR HT SIDE
Is This Answer Correct ? | 85 Yes | 19 No |
Answer / hashim nooruddin
MCCB-- Moulded Case Circket Breaker
ACB -- Air Circket Breaker
VCB -- Vacume Circket Breaker
MCB we use from 0 to 64 Amp.
MCCB we use from 64 to 800 Amp
ACB we use above 800 Amp
More ever at much higher current level we use VCB because
at higher current the air around it get ionised and become
conducter which causes short ckt. so at much higher current
level we generaly use VCB.
Is This Answer Correct ? | 109 Yes | 51 No |
Answer / alan
amazing how much bullsh*t people put up on here about
MCCB/ACB/VCB. be careful when you read the information on
here, and don't trust 100% that the answers given are
correct.
Is This Answer Correct ? | 66 Yes | 17 No |
Since phi is the angular displacement between V & I, then why we use phi in power triangle ie. when showing active, reactive & apperent power in triangular manner & if it is ok then where is V & I in the triangle.
What happened when a three phase induction motor work on two phase supply.9
Send the control circuit digram of a star delta stater?
hi if anybody got model questions for cpcl Grade'A' electrical engineer position.send it to my mail please krishkumar22@gmail.com
What is mean by staling?
how does the switching of capacitors in a capacitor bank take place when we use them at the load side to reduce the power factor?
160 kw motor running use 2R* 150 SQ mm cable
what is the operation of Control Module(CM),MONITOR Module(MM), MONITOR Module DUAL (MM2),Signal Module(SM),Isolator Module(IM), please some one reply me.. the operation and application of these in FIRE ALARM SYSTEMS...
why we use RYB phase sequence? and somewhere we use UVW ? why?
6 Answers CSPDCL-Chhattisgarh State Power Distribution Company Limited, MUET, TCS,
hi every body i am master student in control engineering and my project is slip control in trains i assumed a Dc motore as traction motor but i don't have characteristics of this kind of motor that is used in train. i want from every body if he or she has the characteristics or information about Dc motor that is used in train give me those information or technical characteristics .
What is the method & formula of Fault level calculation in power Transformesr.
what is sevice settings for mccb?How can be it setted?