What is the Difference Between MCCB & ACB & VCB

Answer Posted / kola raju

MCCB: means moulded case circuit breaker which use ark
quenching device as AIR which is used upto 500 Amps only
ACB:air circuit breaker which use quenching device as air
and used upto 3000 Amps at 415 volts
VCB:vaccum circuit breaker which use ark quenching device
as a vaccum and used for 415 volts.6.6 KV,11 KV,33 KV,132
KV,220 KV also.

Is This Answer Correct ?    244 Yes 85 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is the meaning of vcc

1859


How many points does a Circuit can have?

1428


what is formula for calculate thermal overload in new numiricalrelay( not in bimetal relay)?

1764


What are the effects of electrical faults?

577


State kirchoff voltage law?

657






Why squirrel cage motor can only use with low starting loads ?

1527


is there any chart showing the suitable cable size according to AMP and length ? for three phase motors

926


what is the difference between fault current ant short circuit current?

2223


Why are short circuit ratings always 16kA,25kA,36kA and 50kA.Who has fixed these?

3790


Difference between on line capacitor and Station type capacitor

1540


Can a generator runs after getting 1st stator earth fault.

934


What are the conditions to be satisfied for parallel operation of dc generators?

598


What do you understand by oldham's coupling ?

617


hi Is there any possibilities to find out the rotation of a shaft or something else by using electromagnectic waves or by IR rays.If s then can v change the dir., of rotation of the same by remotely?& how? plz dn't any1 say "NO r CAN'T"

1592


Whether 3 phase induction motorwith 100 hp capacity , Amp 160 for which sensitive earth fault relay , type CTUM 15 can be used?

968