What is the Difference Between MCCB & ACB & VCB
Answer Posted / hashim nooruddin
MCCB-- Moulded Case Circket Breaker
ACB -- Air Circket Breaker
VCB -- Vacume Circket Breaker
MCB we use from 0 to 64 Amp.
MCCB we use from 64 to 800 Amp
ACB we use above 800 Amp
More ever at much higher current level we use VCB because
at higher current the air around it get ionised and become
conducter which causes short ckt. so at much higher current
level we generaly use VCB.
Is This Answer Correct ? | 109 Yes | 51 No |
Post New Answer View All Answers
How Diesel Generator start ?
What is the Temperature to be set in Thermostat provided in Marshalling box of the Transformer / Motor.
what is sevice settings for mccb?How can be it setted?
How we can change the direction of rotation of Induction motor? Prove it using graphical
distribution is maximum done by a)radial b)network c) parallel d)b & c
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
We have Diesel generator of 200KW. fuel consumption is always same,even connected light load or full load. Is it right?
How much depth n width required for laying of 1X70 Sqmm Cable in Desert???
Define conversion efficiency of a power amplifier.
Is MEN and RCD related to each other ?? IF yes then how??
how i calculate the syncrones generator NGR resistance .if we have a 6mw generator line voltage of generator 11kv also line current 393.3 ampere.
Don't you have similar question banks related to Oral Certification Examination conducted by Mercantile Marine Departments / Directorate of Shipping, Ministry of Shipping for Electro Technical Officer?
TRANSFORMERS WITH DC SUPPLY
how is capacitor bank look like
how to calculate the size of the HT cable