How can we calculate the fault level of the distribution
system knowing the percentage impedance of transformer &
subsequent equipments.
Answers were Sorted based on User's Feedback
Answer / gopal
fault lavel in MVA= Rated power/% of impedence
or
Fault Lavel= 1.732xFault currentxRated Secondry Voltage
| Is This Answer Correct ? | 69 Yes | 28 No |
Answer / mukul
Dear friends above answer is wrong when you are using
transformer KVA in you calculations then pf is not required
the above answer can be corrected by omitting pf from this calcs
| Is This Answer Correct ? | 44 Yes | 5 No |
Answer / amar singh.
fault level depend on system impedance
full load current*100
Trasformer fault level= ----------------------------
%impedance of the transformer
| Is This Answer Correct ? | 51 Yes | 17 No |
Answer / pankaj
THERE IS A SIMPLE CALCULATION IF ASSUMING INFINITE SOURCE
BUS THE MAX LEVEL OF FAULT AT LT SIDE OF A 11/0.433 5%
1000KVA TRANSFORMER CAN BE CALCULATED AS:
KVA*100/SQRT3*433*Z% kAMPS
1000*100/1.732*433*5 = 26.7kAMS
| Is This Answer Correct ? | 39 Yes | 7 No |
Answer / k n naidu
hi,
Calculation of fault level of a distribution net work of
complex in nature manually is laborious. Use network
analyser for simulating the network and fault at the
required bus to get the fault current.
for manual calculation use the MVA method which is
simple and gives fairly acurate results
| Is This Answer Correct ? | 23 Yes | 7 No |
Answer / leonard
Fault level = Rated Voltage / system impedence (up to that
point)
transformer impedance can be calculated using the
following formula:
Z(transformer)=(Vsq*Z%)/(P*100)
where
Ztransformer is the source transformer impedance, in ohms;
P is the power of the transformer, in volt amperes;
Z% is the rated short-circuit impedance voltage of the
transformer, expressed as a percentage.
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / abhi
Fault level = (Rated power of transformer*100)/(percentage
impedance of transformer + imp of subsequent equipments)
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / jojo
rated capacity of transformer divide by its transformer
impedance.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / avatar
When deciding the fault levels, isnt there a time component
as well? I have seen the fault levels being designated
as "350 MVA @ 1 sec". What does this mean? Please help.
| Is This Answer Correct ? | 3 Yes | 3 No |
What is the type of electrical motor used in mining industries?
Your B.tech marks is being given in CGPA grade. How is it calculated?
how the direction relay sense rhe directional fault?it's forward or reverse?
How electrical power is generated by an A.C Generator ?
Why the transformers are rating in KVA.?
it is clear that volts equal to the current as per ohms law. is it appliable to the AC power or only for DC. if it is appliacable to AC in transformers when voltage increases the voltage decreases ????? why??????????????
What is a compensator?
what is induction relay
What is the electrical difference between Earthing Switch (ES) and Maintenance Earthing Switch (MES)?
can any one suggest websites having study maetrials for the electrical students?
why do we provide metallic enclosure to bus duct and then ground it?
slor cell made?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)