if we known the pesentage of impedance then by using this
formula we can calculate the fault Lavel.
fault lavel in MVA= Rated KVa/% of Impedence
OR
Fault Lavel= 1.732xFault Currentx Rated Voltage
| Is This Answer Correct ? | 146 Yes | 38 No |
Post New Answer View All Answers
why is a power transformer used only occasionally?it is used to step up at generating stations?and that needs to be done all day long !!!!!!!
How to configure the drives in PLC, through Profibus commnication. And to how to address it?
kindly send me 11KV MV motor differential protection procedure by primary injection method.
rajha power sector details
Dear all, how we select the cable size according to current with or without including different correction factor , is there any direct method for sizing of cable...
Is there possible to Test Transformer for Overfluxing Capability. Or is there any firm who does Overfluxing Test on Transformer?
what is control supply rating of a machine
Explain about Leakage Test.
What are differences between Voltage, EMF & Potential difference ?
Please define ohm’s law for a.c (alternating current)?
What are the relays in ACB and VCB
Initially, when the input is not equal to the output — what type of response is this?
Classify milling machines.
What will be advantage if we put some load in neutral of grounded star transformer & loadshortcircuit current,rated current of cable & MCB with example?
what's prime importance of protection in electrical system.if protection system don't work properly what can happen in electrical system?