In step down transformer (415/200V),mistakenly secondary
side is connected to 415V for some hours, what would be
result of this condition?
Answers were Sorted based on User's Feedback
Answer / ankaraju
The secondary side is rating of 200v,if you considering
loop the net current flowing throw winding increases hence
losses also increases and winding over heated,if it so on
for hours winding insulation may failed.And another one is
core is nearer to low winding,due to high voltage core
losses and core insulation between laminations also failed.
| Is This Answer Correct ? | 34 Yes | 5 No |
Answer / milan
secondary side winding turns is designed for 200 volts. If
we give 415v the secondary side winding turns will not
sustain the voltage . For which insulation and winding both
will damage .If we give 415v to secondary the primary will
get 816.125v
| Is This Answer Correct ? | 19 Yes | 3 No |
The current at 200v side will be more than what designed
for the transformer and core loss will be more. So
ultimately,transformer will be heated up more faster than
ordinary condition. Depends upon the insulation used for
core construction, and how long u are connected the supply,
there r chances of insulation failiure.
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / manoj
as 2ndary side winding is design for 2oo volt so when we
connect 2ndary side to 415 volt,then after some hour the
2ndary winding burnt.
| Is This Answer Correct ? | 9 Yes | 4 No |
Answer / neeraj
the whole transformer will burn up.
i do it practical one time.
but in future i will not do such thing.
| Is This Answer Correct ? | 4 Yes | 1 No |
if Secondary puts 415v, than primary wants to take the
voltage upto 850v, & it can burn the winding of the
transformer.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / partha
In this case, the transformer will undergo insulation
degradation. Also due to the increased voltage, the core
losses will increase. The core will be also subjected to
overfluxing which will cause saturation and increased core
losses.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vino raju dee
200v induced in the primary.there is no application for
this induced voltage.
| Is This Answer Correct ? | 0 Yes | 0 No |
Why efficiency in thermal power plant is low?
What is the meaning of CT 40/5, 100/5 or in HT lines 100/1 ????????
what will happen if we directly give supply to rotor of a induction motor?
In case of legging current of 20°, pf is .94 and leading of 20°,pf is .94 , in mathematicaly both are same but in realy how it is differ ?
how to maintain standard votage in power system?
why the single phse machine can not run by the three phase supply.
WTA used cb?
substation+ plc system
how to calculate power loss cost of aluminium conductor and copper conductor?500v,100A,68mm area squre busbar.
what is the use of conservator in a transformer?
6 Answers L&T, TATA, Tata Motors,
1- XC and the RC time constant are both measures of the reaction of C to a change in ____? 2-The power factor is a numerical ratio with a value between 0 and 1 equal to the ______________ of the phase angle. 3-When V and I are out of phase because of reactance, the product of V times I is called ______________ power 4-For _____________ inductors, the branch currents can be added algebraically. 5- The ______________ power in watts can be calculated as I^2R 6-Calculate XL with L = 30mH and f = 1kHz ( I have Xl=2piFL 2*3.141592653*1kHz*30mH =188 ohms Please check) 7-A parallel RL circuit has the values, R = 5kohms, XL = 5kohms. A voltage source of Vt = 10Vrms is connected in parallel to R and L. Determine the total current, It delivered by the voltage source Vt. 8-A series RC circuit has R = 1Mohm and C = 1microF. How long would it take for the capacitor to fully discharge if it is initially fully charged? 9-A circuit has real power = 300W and an apparent power of 500VA. Determine the power factor and phase angle. 10-The time constant for an LR series circuit is T = 0.1s and R = 10ohms. Calculate the inductance L.
TO operate transformers in parallel, vector symbol of the both should be same.If one transformer name plate is not there, how can we conclude that whether the transformer is having the same vector symbol or not?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)