what is pf. how to calculate capacitor bank value to
maintain unity pf.
Answers were Sorted based on User's Feedback
Answer / nilesh kumar singh
Power Factor is defined as the ratio of Real power and
Apparent power.
for calculating Capacitor bank value the formula is :
kVAr = KW {tan(cos^-1 Phi e) - tan(Cos^-1 Phi d)}
Where - Phi e = existing Power Factor.
Phi d = Desired Power Factor.
| Is This Answer Correct ? | 101 Yes | 8 No |
Answer / rajendra singh
for calculating Capacitor bank value the formula is :
kVAr = KW {tan(cos^-1 Phi e) - tan(Cos^-1 Phi d)}
Where - Phi e = existing Power Factor.
Phi d = Desired Power Factor.
| Is This Answer Correct ? | 42 Yes | 8 No |
Answer / shivappa
to calculate desired capacitor value, the formula is
KVAR= KW(TAN PHI 1 - TAN PHI 2 )
WHERE PHI 1 = EXISTING POWER FACTOR
PHI 2 = REQUIRED POWER FACTOR
| Is This Answer Correct ? | 23 Yes | 14 No |
Answer / kim leang
KVAR= KW(TAN PHI 1 - TAN PHI 2 )
WHERE PHI 1 = EXISTING POWER FACTOR
PHI 2 = REQUIRED POWER FACTOR
| Is This Answer Correct ? | 14 Yes | 9 No |
Answer / midhun
Calculation and selection of required capacitor rating
Qc = P * {tan [acos (pf1)] - tan [ acos (pf2)]}
Qc = required capacitor output (kVAr)
pf1 = actual power factor
pf2 = target power factor
P = real power (kW)
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / fancy102
hi..i also interested in it..i am carrying out pf
measurement system and i am headache in how to maintain the
unity pf too..
| Is This Answer Correct ? | 40 Yes | 36 No |
Answer / ezzuddin
The correct answer and below is the proof of the formula:
KVAR= KW X [√(1–(COSФ)^2)]/COSФ
The proof:
Pythagoras Theorem states that in a right-angled triangle
the square of the hypotenuse is equal to the sum of the
squares of the other two sides.
so that:
Q is the hypotenuse.
S is the opposite.
P is the adjacent.
TanФ= opposite/adjacent = S/P -----> S=P x(TanФ)
Pf=COSФ= adjacent/hypotenuse = P/Q ---->Q=P/COSФ
Pythagoras said that:
Q^2= P^2 + S^2
P^2/(COSФ)^2= P^2 + (P^2 x (TanФ)^2)
by divide P^2:
1/(COSФ)^2 = 1 + (TanФ)^2
by changing the both sides:
(TanФ)^2 = (1/(COSФ)^2) - 1
(TanФ)^2 = (1/(COSФ)^2) - ((COSФ)^2/(COSФ)^2)
by Taking the (1/(COSФ)^2) Common factor:
(TanФ)^2 = {1/(COSФ)^2)} x ( 1 - (COSФ)^2)
by taking the square root:
TanФ = [√(1–(COSФ)^2)]/COSФ
so that:
KVAR = KW x [√(1–(COSФ)^2)]/COSФ
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / santosh
react power kvar=v i sin phi, we know p.f=1,i.e cos phi
calculate sin phi,v i values from total load
| Is This Answer Correct ? | 14 Yes | 11 No |
Answer / vekuva
KVAR= KW(TAN PHI 1 - TAN PHI 2 )
WHERE PHI 1 = EXISTING POWER FACTOR ANGLE i.e., COS^¯1(p.f1)
PHI 2 = REQUIRED POWER FACTOR ANGLE i.e., COS^¯1(p.f2)
p.f 1 = EXISTING POWER FACTOR
p.f 2 = REQUIRED POWER FACTOR
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / ezzuddin
The correct answer and below is the proof of the formula:
KVAR= KW X [Sqrt(1–(CosQ)^2)]/CosQ;
The proof:
Pythagoras Theorem states that in a right-angled triangle
the square of the hypotenuse is equal to the sum of the
squares of the other two sides.
so that:
C is the hypotenuse.
S is the opposite.
P is the adjacent.
TanQ= opposite/adjacent = S/P -----> S=P x(TanQ;)
Pf=CosQ;= adjacent/hypotenuse = P/C ---->C=P/CosQ;
Pythagoras said that:
C^2= P^2 + S^2
P^2/(CosQ)^2= P^2 + (P^2 x (TanQ)^2)
by divide P^2:
1/(CosQ)^2 = 1 + (TanQ)^2
by changing the both sides:
(TanQ)^2 = (1/(CosQ)^2) - 1
(TanQ)^2 = (1/(CosQ)^2) - ((CosQ)^2/(CosQ)^2)
by Taking the (1/(COSQ)^2) Common factor:
(TanQ)^2 = {1/(CosQ)^2)} x ( 1 - (CosQ)^2)
by taking the square root:
TanQ; = [Sqrt(1–(CosQ)^2)]/CosQ;
so that:
KVAR = KW x [Sqrt(1–(CosQ)^2)]/CosQ;
| Is This Answer Correct ? | 4 Yes | 1 No |
We have 2 11kv/433v transformers for 2saperate acb for mv panels and 1 bus coupler acb. Suppose I’ll close bus coupler what will happen or it will be share the load. Please suggestion and any modification required.
HRC full from
what is the meaning of 1250 KVA Trasformer
Explain the operation carried out in thermal power stations?
What happen if ac supply is fed to rotor of the alternator?
How to calculate ht side cable of 630 kva oil cooled outdoor transformer?
why motor burns ?
I want to know that a 160kva diesel generator contains capacity of 160kva on each phase like R=160 Y=160 B=160 total RYB=480kva or it is total capacity of all there phases like RYB=160kva ... thanks in advance ...
2 Answers jlpl, JP Saraswat Engineers,
What is the resonant peak?
USE OF 8 WAY PAN ASSEMBLY
In ups static switch if i gives the supply at output end it will open the circuit in stactic switch or not if it will open then how it operates.
does not the circulating current in a transformer affect the flux distribution in the transformer core
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)