Answer / nilesh kumar singh
Power Factor is defined as the ratio of Real power and
Apparent power.
for calculating Capacitor bank value the formula is :
kVAr = KW {tan(cos^-1 Phi e) - tan(Cos^-1 Phi d)}
Where - Phi e = existing Power Factor.
Phi d = Desired Power Factor.
Is This Answer Correct ? | 101 Yes | 8 No |
Answer / rajendra singh
for calculating Capacitor bank value the formula is :
kVAr = KW {tan(cos^-1 Phi e) - tan(Cos^-1 Phi d)}
Where - Phi e = existing Power Factor.
Phi d = Desired Power Factor.
Is This Answer Correct ? | 42 Yes | 8 No |
Answer / shivappa
to calculate desired capacitor value, the formula is
KVAR= KW(TAN PHI 1 - TAN PHI 2 )
WHERE PHI 1 = EXISTING POWER FACTOR
PHI 2 = REQUIRED POWER FACTOR
Is This Answer Correct ? | 23 Yes | 14 No |
Answer / kim leang
KVAR= KW(TAN PHI 1 - TAN PHI 2 )
WHERE PHI 1 = EXISTING POWER FACTOR
PHI 2 = REQUIRED POWER FACTOR
Is This Answer Correct ? | 14 Yes | 9 No |
Answer / midhun
Calculation and selection of required capacitor rating
Qc = P * {tan [acos (pf1)] - tan [ acos (pf2)]}
Qc = required capacitor output (kVAr)
pf1 = actual power factor
pf2 = target power factor
P = real power (kW)
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / fancy102
hi..i also interested in it..i am carrying out pf
measurement system and i am headache in how to maintain the
unity pf too..
Is This Answer Correct ? | 40 Yes | 36 No |
Answer / ezzuddin
The correct answer and below is the proof of the formula:
KVAR= KW X [√(1–(COSФ)^2)]/COSФ
The proof:
Pythagoras Theorem states that in a right-angled triangle
the square of the hypotenuse is equal to the sum of the
squares of the other two sides.
so that:
Q is the hypotenuse.
S is the opposite.
P is the adjacent.
TanФ= opposite/adjacent = S/P -----> S=P x(TanФ)
Pf=COSФ= adjacent/hypotenuse = P/Q ---->Q=P/COSФ
Pythagoras said that:
Q^2= P^2 + S^2
P^2/(COSФ)^2= P^2 + (P^2 x (TanФ)^2)
by divide P^2:
1/(COSФ)^2 = 1 + (TanФ)^2
by changing the both sides:
(TanФ)^2 = (1/(COSФ)^2) - 1
(TanФ)^2 = (1/(COSФ)^2) - ((COSФ)^2/(COSФ)^2)
by Taking the (1/(COSФ)^2) Common factor:
(TanФ)^2 = {1/(COSФ)^2)} x ( 1 - (COSФ)^2)
by taking the square root:
TanФ = [√(1–(COSФ)^2)]/COSФ
so that:
KVAR = KW x [√(1–(COSФ)^2)]/COSФ
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / santosh
react power kvar=v i sin phi, we know p.f=1,i.e cos phi
calculate sin phi,v i values from total load
Is This Answer Correct ? | 14 Yes | 11 No |
Answer / vekuva
KVAR= KW(TAN PHI 1 - TAN PHI 2 )
WHERE PHI 1 = EXISTING POWER FACTOR ANGLE i.e., COS^¯1(p.f1)
PHI 2 = REQUIRED POWER FACTOR ANGLE i.e., COS^¯1(p.f2)
p.f 1 = EXISTING POWER FACTOR
p.f 2 = REQUIRED POWER FACTOR
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / ezzuddin
The correct answer and below is the proof of the formula:
KVAR= KW X [Sqrt(1–(CosQ)^2)]/CosQ;
The proof:
Pythagoras Theorem states that in a right-angled triangle
the square of the hypotenuse is equal to the sum of the
squares of the other two sides.
so that:
C is the hypotenuse.
S is the opposite.
P is the adjacent.
TanQ= opposite/adjacent = S/P -----> S=P x(TanQ;)
Pf=CosQ;= adjacent/hypotenuse = P/C ---->C=P/CosQ;
Pythagoras said that:
C^2= P^2 + S^2
P^2/(CosQ)^2= P^2 + (P^2 x (TanQ)^2)
by divide P^2:
1/(CosQ)^2 = 1 + (TanQ)^2
by changing the both sides:
(TanQ)^2 = (1/(CosQ)^2) - 1
(TanQ)^2 = (1/(CosQ)^2) - ((CosQ)^2/(CosQ)^2)
by Taking the (1/(COSQ)^2) Common factor:
(TanQ)^2 = {1/(CosQ)^2)} x ( 1 - (CosQ)^2)
by taking the square root:
TanQ; = [Sqrt(1–(CosQ)^2)]/CosQ;
so that:
KVAR = KW x [Sqrt(1–(CosQ)^2)]/CosQ;
Is This Answer Correct ? | 4 Yes | 1 No |
how to save the power?
Which type of losses in transmission Line
What do you mean by PT-100?
purpose of breaker contact multiplication relay?
What is the normal value of delta in rotor angle stability or transient stability? Why it selected so?
What will happen if we on 200kvr capacitor bank(11kv in bus)If there is low load on transformer (1.5 mva 33/11 kv)
what are the effects on an power plant and consumers if the power factor is increased or decreased?
Why HT cable have only 3 core ?
why +24 v and -48 v give to BTS? If -48v protect from surge then why we not use -24 v?
What is the GI Earth Flat Size recomended for 33KV 2000KVA Distribution Transformer
what use marshalling kishock in power transformer?
What is relation b/w Transmission Lines & Communication Lines ?