what is pf. how to calculate capacitor bank value to
maintain unity pf.
Answers were Sorted based on User's Feedback
Answer / shashikant
CALCULATIONS AND TABLES
Calculation and selection of required capacitor rating
Qc = P * {tan [acos (pf1)] - tan [ acos (pf2)]}
Qc = required capacitor output (kVAr)
pf1 = actual power factor
pf2 = target power factor
P = real power (kW)
The table below shows the values for typical power factors
in accordance with the above formula
TARGET POWER FACTOR
0.7 0.75 0.8 0.85 0.9 0.92 0.94 0.96 0.98 1
Actual Power Factor
0,40 1.27 1.41 1.54 1.67 1.81 1.87 1.93 2 2.09 2.29
0,45 0.96 1.1 1.23 1.36 1.5 1.56 1.62 1.69 1.78 1.98
0.50 0.71 0.85 0.98 1.11 1.25 1.31 1.37 1.44 1.53 1.73
0,55 0.5 0.64 0.77 0.9 1.03 1.09 1.16 1.23 1.32 1.52
0,60 0.31 0.45 0.58 0.71 0.85 0.91 0.97 1.04 1.13 1.33
0,65 0.15 0.29 0.42 0.55 0.68 0.74 0.81 0.88 0.97 1.17
0,70 0 0.14 0.27 0.4 0.54 0.59 0.66 0.73 0.82 1.02
0.75 0 0.13 0.26 0.4 0.46 0.52 0.59 0.68 0.88
0,80 0 0.13 0.27 0.32 0.39 0.46 0.55 0.75
0.85 0 0.14 0.19 0.26 0.33 0.42 0.62
0,90 0 0.06 0.12 0.19 0.28 0.48
The required capacitor output may be calculated as follows:
select the factor (matching point of actual and target
power factor) k
calculate the required capacitor rating with the formula:
Qc = k * P
Example:
actual power factor = 0.70, target power factor = 0.96,
real power = P = 500kW,
Qc = k * P = 0.73 * 500kW = 365 kVAR
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / cbc
1. PF=Real Power/Apparent Power or PF=KW/KVA
2. a.) (KVAR1)*2 = (KVA1)*2 - (KW1)*2
b.) (KVAR2)*2 = (KVA2)*2 - (KW1)*2
c.) REQ'D KVAR= KVAR1-KVAR2
Is This Answer Correct ? | 5 Yes | 4 No |
Answer / ezzuddin
SORRY FOR THE ABOVE WRONG INFO AND The correct answer AS
STATED below is the proof of the formula:
KVAR= MAX Demand X [TanQ1 - TANQ2];
TanQ1= [Sqrt(1–(CosQ1)^2)]/CosQ1
TanQ2= [Sqrt(1–(CosQ2)^2)]/CosQ2
The proof:
Pythagoras Theorem states that in a right-angled triangle
the square of the hypotenuse is equal to the sum of the
squares of the other two sides.
so that:
C is the hypotenuse.
S is the opposite.
P is the adjacent.
TanQ= opposite/adjacent = S/P -----> S=P x(TanQ;)
Pf=CosQ;= adjacent/hypotenuse = P/C ---->C=P/CosQ;
Pythagoras said that:
C^2= P^2 + S^2
P^2/(CosQ)^2= P^2 + (P^2 x (TanQ)^2)
by divide P^2:
1/(CosQ)^2 = 1 + (TanQ)^2
by changing the both sides:
(TanQ)^2 = (1/(CosQ)^2) - 1
(TanQ)^2 = (1/(CosQ)^2) - ((CosQ)^2/(CosQ)^2)
by Taking the (1/(COSQ)^2) Common factor:
(TanQ)^2 = {1/(CosQ)^2)} x ( 1 - (CosQ)^2)
by taking the square root:
TanQ; = [Sqrt(1–(CosQ)^2)]/CosQ;
so that:
KVAR = KW x [TanQ1 - TANQ2]
example:
PF1 = CosQ1 = 0.8
PF2 = CosQ2 = 0.92
TanQ1 = 0.75
TanQ2 = 0.426
P=1000 KW
Max Demand = 1000x0.8= 800 kW
Capacity of the required Capacitor= 800 x(0.75 - 0.426)=
264 KVAR
We proposed automatic capacitor= 300 KVAR
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / sm
pf is the cosine of the angle b/w voltage phasor and current phasor. To maintain unity feedback the capacitor bank value should be such that it compensates the inductive reactance value in circuit i.e., X becomes zero. Thus, the circuit becomes purely resistive and pf is unity.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rukmagoud
Required Capacitor bank and required KVAR of the bank to be
installed to improve power factor from say x to y is
KVAR=KW(TANx-tany).This can be better understood from power
triangle.
RUKMAGOUD
APGENCO
HYD
Is This Answer Correct ? | 3 Yes | 4 No |
Answer / udayak25
in short I tell u -
kVA
kVAR = -----
0.432
it gives u a correct value of capacitor bank.
-Uday
Is This Answer Correct ? | 4 Yes | 6 No |
Answer / j. nagarajan
The power factor is the ratio of voltage to current at
120Deg Phase shift.
Cos phi = KVA/KW
The active power factor in our country will be 0.8 only, ie
only 80% of power consumed and balance is lost due to
various lossed in the distribution system.
To calculate Cap. bank the formula is
KVAR = Power tan (cos phi(ext)-tan cos phi (exp)
where cos phi(ext) - existing power factor & exp is
expecting power factor.
It is not possible to brought to unity powerfactor is
utilising 100% of power to the application. Max. of 95% can
be possible for which the power factor value will be 0.95
After calculating cap. banks, say 100kvar, it can be
seperated like below:
1:1:1:1 (where 1=25kvar)
1:2:1(where 2=50kvar)... and so on.
- J. Nagarajan
Is This Answer Correct ? | 0 Yes | 4 No |
Answer / hassan azzam
dear all your formula is correct but this for existing
system , wher if you dont have mesured value how to estimat
there use my estimation
Qc (Kvar) = connected load( kw)* 0.8 * 0.75 * 0.421
Qc (Kvar) = connected load (kw) * 0.2526
this is for future load or testing and commissioning perid
Is This Answer Correct ? | 5 Yes | 10 No |
how induction generator generated the power without excition like syncronous generator.
What is the use of Isolation Transformer, and Neutral is using for return path, finally this current is going.... but same time the voltage of the neutral should be below 1 V...
Why transformer neutral earthing? What is advantages?
Define conversion efficiency of a power amplifier. What is its value for class c power amplifier?
Write a note on materials used as a fuse element.
what will happen while giving 2 phase supply to 3 phase motor
What value(high/low) of diversity factor is desired in power system and why? How such value is achieved?
in 1-phase 230v,how in 3-phase 440v. in each phase in between 230v.
I need to compare the energy consumption of an industrial machine before and after improving. Shall I compare the apparent power or the active power? I know usually factories use compensated capacitors (or other similar components) to compensate the reactive power, so if I use the apparent power, it's not the real power consumed.
How to calculate meter constant @ HT yard
WHAT ARE THE EFFECTS OF SERIES RESONANCE AND PARALLEL RESONANCE ON THE CIRCUITS PARAMETERS?
How can we explain that what is the power factor?