How to calibrate level switch?
Answers were Sorted based on User's Feedback
Suppose you using Float/ displacer type of level switch.
Do the followings:
1. Fill the process into chamber of level switching mark.
2. Contacts of level switch should be changed.
3. If already, closed contacts, then should change to open condition.
4. If contacts not changing, do the knob of switch to change.
Suppose you can not fill process into chamber.(Process may harmful, like ammonia etc).
1. Note the process specific gravity. Suppose it is 0.67.
2. Your height for level switching is 1000 mm.
3. Use water to fill into chamber for calibration instead of process.
4. 1000 x 0.67 = 670 mm
5. So fill into chamber up to 670 mm water. It will operate the switch.
aftabmazari@yahoo.com
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / mahalingam
The switches all are working in Digital mode.Like 0 or 1. To do the calibration confirm the NO & NC. Basically it is NC when the process reaches the desired level then the circuit will be NO.
| Is This Answer Correct ? | 0 Yes | 2 No |
What is the differerence between hysterisis and linearity.
what is the difference between magnetic flow meter and mass flowmeter
how to set calibration range in a DP transmitter to measure level for a closed tank and for an open tank,and also please explain me how to set calibration range for a DP flow transmitter in a line ?
HOW WE MEASURE A DRUM LEVEL BY DP TRANSMITTER ? WHAT IS ITS FORMULA ?
working principle of lvdt?
what is the meaning of wet leg & where is it used?
what is the output of conductivity sensor and PH sensor?
Specify for Cables - Flame Retardant and Fire Resistant?
Thermocouple is a transducer but rtd is not transducer why? Both taking heat as a input and giving mv
how the actually positioner of control valve working? where we gave 3-15psi pressure to I/P converter where it is firstly applied ?- on I/P to positioner then what happen? is control valve operate on 3-15 psi or its bench pressure?
For what reason would you possibly be compelled to make use of a Smith Predictor. Explain the idea behind the operation of this device.
How addressable fire systems work? Pl. send details with architect.(Loop), also send details regarding Gas system. Pl. help me.Thanks
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)