Answer / carl_ellis

Configuring the range for a DP transmitter

Open tank:
- Flanged DP transmitter
- high side at lower flange
- no remote seals:
- units: water column units = uwc
- LRV = 0.00 uwc
- URV = physical upper level elevation (uwc) * specific
gravity of fluid

Closed tank:
- flanged DP transmitter
- high side at lower flange
- no remote seals
- dry leg from vapor space above liquid is piped/connected
to the low side
- LRV = 0.00 uwc
- URV = physical upper level elevation (uwc) * specific
gravity of fluid

When the receiver (DCS/PLC/indicator/recorder) receives the
level signal, it converts to physical level elevation by
dividing the process level signal by the specific gravity
and scaling to physical level units.

Volumetric flow rate with DP transmitter on DP flow element:
- units: water column units = uwc
- LRV = 0.00
- URV = maximum DP value at the maximum flow rate stated
on the sizing sheet of the DP flow element

Whether the signal is square rooted in the transmitter or
in the receiver for conversion to flow rate is up to the
plant convention/standards.

Is This Answer Correct ?    2 Yes 5 No

Post New Answer

More Instrumentation Interview Questions

Define the terms Accuracy, precission, Spam, process tolerance while doing calibration of an instrument? Explaini with an example?

0 Answers   AquaTech,


WHY WE R NOT USING THE TURBINE FLOW METER IN THE STREAM SERVICE ? pl explain?

3 Answers  


How to work & calculated output of the Derivative action in pid controller (Explain Derivative controller)

0 Answers  


3element

2 Answers  


WHAT IS THE VALUE OF MICRON

2 Answers  






what is the T/C & RTD mesuremaint?

3 Answers  


why does mA signal preferred for signal transmission?

12 Answers   Emerson,


What is modbus?

0 Answers  


How to regulate the flow of Air in 4" line, with max flow of 330 nm3/hr and Pressure of 0.5 bar? please suggest the type of instrument required.

0 Answers  


What is three element in drum level?

0 Answers  


key phaser where is use and work

0 Answers   BAP,


Can anyone say that formula of Converting the Diff. Pressure into Flow in Kg/Cm2 or any explaniation of Orifice Plate, Beta Ratio , How to calculate

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)