what are the possible reasons if a control valve fails to open/close?
Answer / carl_ellis
I seen 10 to 20 causes for each of these categories, but
I've only listed one as an example.
Reasons for valve not closing or opening:
intentional or unintentional
- lack of energy - air/electric/hydraulic (Fuse blown)
- insufficient energy - (supply air regulator turned down)
- control system issue (control signal interlocked)
- positioner or I/P issue (locked in manual)
- actuator crippled (punctured diaphragm)
- positioner-to-actuator linkage/plumbing issue (tubing failed)
- actuator-to-valve linkage issue (sheared roll pin)
- valve trim damage
- foreign object blocking movement (how does all that junk
get in the piping in the first place?)
- change in design process conditions (actuator can't close
against increased line pressure)
Not all failures to actuate/move are faults - a valve could
be intentionally locked in place for safety reasons - access
to the piping/tank.
Tell 'em Carl sent you.
Is This Answer Correct ? | 15 Yes | 0 No |
WHAT REASEAN USE TRANSMETER TWO WIRE & FOUR WIRE
You are looking at the RS-485-side of an RS-232/RS-485 converter and the power supply voltage for the converter is +5V. Under idle conditions (no transmission), and assuming you have enabled the RS-485 output: what would you expect at: (a) Output A measured against output B (b) Output A measured against ground (c) Output B measured against ground
Is Hart communicator calibration device or communicating device for transmitter?
How to find out turn down ratio of Pressure transmitter?
What is the relationship between GAIN and PROPORTIONAL BAND.
1 Answers Kharafi National, Sabic,
how works encoder in plc
how will do square root transmitter calibration
how to write the program for single push button by using ladder diagram
What is the difference between rich gas and lean gas?
What is Loop Test & What is Loop Checking? Please i need answer for these questions.
What is eddy current? Describe the operating principle of proximity probe.
can we replace a slot sensor (inductive type) with limit switch (potenial free contact / no-nc type).