in instrumentation why we are using 4-20mA , why not
voltage ? if somebody design a instrument which works on
voltage then can we use that instrument?
Answers were Sorted based on User's Feedback
Answer / bnp
because there is voltage drop as per the length of conducting wire. but current has no drop
| Is This Answer Correct ? | 16 Yes | 0 No |
Answer / pradeep patil
Current 4-20 mA is prefered than voltage because:--
1)current signal can be carried to long distance without
drop in signal strength.
2)Less Electro Magnetic Interference effect in current
signal
3)no short crcuit spark happpens when signal cable
accidently short each other.
If your controller works on voltage (1-5 vdc) then 4-20 mA
can be easily converted in to voltage after connecting 250
ohm resistance accross signal cable as per ohms law.
| Is This Answer Correct ? | 14 Yes | 0 No |
Answer / himanshu
4-20 mamps is best choice because interference level is
minimum in current application where as in 0-10 V it is
comparatively high.Thus in using 4-20 mamps signal is
distortionless.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / b0nz0
Most of the above answers are valid, but none have
mentioned security. If a current loop is broken then the
current will fall to 0.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / yogi40
if we use voltage there there is noise interpretation
where as in current it wont happen
and current supports 2 wire connection,voltage doesnt
there will be drop in voltage when its feedback in current
such loss is very less
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / manuraj singh sengar
no, because voltage makes fluctuation & current remains
constant.
| Is This Answer Correct ? | 0 Yes | 12 No |
what is differance between SOE an alarams
what is the deference bitween DCS and PLC SCADA HMI System for Power Process Industry.
what is the diffrene between DCS System and PLC System
what is the main supply source for pressure transmitter?
Draw a P& ID showing – orifice flange, plate, dp transmitter, isolation & bypass valves and tubing.
What is the use instrument barriers? Can you give me review materials about this?
how can you change unit of totalizer in siemens mag 5000 flow meter?
What is the diffrence between digital signal processing and discrete signal processing?
difference between null and deflecting instrument.
what are the levels of automation?
What safety precautions you will adopt to work on Steam service control valve?
which type of rtd is good for any system,2wire,3wire or 4 wire
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)