In transformer which temp should be less oil temp are
winding temp?
Answers were Sorted based on User's Feedback
Answer / sathiyamurugna
normally oil temperature should be less compared to winding
temperature because transformer oil used for cooling the
winding. if oil temperature should not go high other wise it
will not cool the winding properly
| Is This Answer Correct ? | 39 Yes | 0 No |
Answer / vishal ingle
in normal condition, oil temperature should be less
compared to winding temperature because transformer oil is
used for cooling the winding. oil takes away the heat from
winding resulting in reduction of temperature. Also for
natural heat flow the oil temperature should be less than
winding temperature.
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / siddesh cs
under normal condition,transformer oil as low temperature compared to lv & hv winding because, oil is mainly used for cooling purpose as per the law of thermodynamics heat flows from hot end to coold end so heat transfer from winding to oil.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / karthik
should be oil temp is less, oil is used for cooling the transformer
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / prabhakar jha
oil temperature should be less then winding temperature.winding temperature depends on Load.so oil temperature should be less for cooling transformer winding..
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pritesh
Obviously Oli temperature should be less than winding temperature because oil immersed tc oil basically use for heat dissipation and cooling so oil temp less
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / anupama
the external or u can say the temprature of ur surrounding
should be less than both because ultimately heat is
disspated in surroundingsss
| Is This Answer Correct ? | 0 Yes | 2 No |
In constant power region of 3-phase IM torque-speed characteristics, if frequency increases voltage A does not alter B decreases C increases D none of above
Whether amorphous core transformer is available in India?.If available then up to what rating of voltage and KVA?.
0 Answers DAE, Tata Chemicals,
What is duty cycle and protection class?
avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid after synchronisation it regulates power factor why....
Why D.C Voltage used in Meggering...as well as in Hipot test? why not A.C?
what are check points to be checked while charging switchyard?(CT,PT,BREAKER,POWER TRANSFORMER)
method to check earthing
Why a transformer Noise during its running condition ?
1.How to calculate backup time from series connected battery of 12v dc with 26Ah for 2battery?
what meant by Locked Rotor Current ?
say a transformer is designed for 33/11kv step down with ratio 0.33 for load 1 mva. if am giving 11kv as a input that same transformer what will happen to its o/p voltage. and whether it can be operated for 500kva
how to test the ht machines?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)