Answer / k.prakashchandra
AVR maintains the set voltage and does not regulate it.APF
mode is an option in Auto- channel in addition to AVR mode
and it is put in action after synchronization.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
After synch,AVR keeps the gen voltage constant at the set
value. If the grid voltage is more than the gen voltage, the
pf becomes leading and lagging if the grid voltage is less
than the gen voltage.Then, in AVR mode the operator has to
reset the gen voltage so that the pf is slightly lagging.In
APF mode ,the pf always remains at the set value
irrespective of variations in grid voltage.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mohammed sajid
I can't understand your language mr.prakash,just explain
what is the function of AVR before & after synchronisation
with grid.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / balu
Once the generator connects with the grid the system voltage depends upon to the grid referrence.the active power varies depends on the load.so load varies mean time reactive power also variey.so avr will maintaine power factor after synchronization.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
It is possible to have the changeover from AVR to APF mode
automatically on synchronization / closing unit CB and the
vice versa, using auxiliary switch of the breaker.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
It keeps the gen voltage the same at the set value
irrespective of variation in speed , load and grid voltage
after synchronization. It is useful whenever there is grid
failure as the gen speed suddenly increases to an extent
depending on the load interrupted.Then AVR does not allow
for rise in voltage.It is also very helpful while
synchronizing as you do not have to vary the excitation
every now and then ,once you have matched the voltages.If
you desire to keep the pf constant after synch and loading
,you have to switch over to APF mode from AVR ,both being
available with Auto channel.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / it might be for easy calculati
It might be for
easy
calculation:-)
| Is This Answer Correct ? | 2 Yes | 3 No |
What is the difference between synchronous asynchronous memory?
Which type of control system is expensive — closed loop or open loop?
What is maximum load capacity of 800 VA inverter?
What is generator
How power is transferred from one winding to another in an auto-transformer? A) electrically B) magnetically C( both a & b D) neither of above
What are the site acceptance tests for power cables, DG Sets, LT panels & 30kVA UPS ?
in 31.5 mva power transformer how to set of wti and oti?
explain why reduced voltage starters are required for large tree phase inudction motor
will we have to design the UPS differently for both i.e. if we want to connect the two batteries in parallel and/or we want to connect the two batteries in series ?
what is the AC Plant and how can do the work with parts and picture tell us 150 Tr
On a 6 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 42 AH). What Shall be the current rating of DC MCB ?
0 Answers TNEB Tamil Nadu Electricity Board,
What types of I/O have you designed? What were their size? Speed? Configuration? Voltage requirements? Process technology? What package was used and how did you model the package/system? What parasitic effects were considered?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)