avr is an automayic voltage regulator ... it regulates
voltage before it synchronise with grid after
synchronisation it regulates power factor why....
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
AVR maintains the set voltage and does not regulate it.APF
mode is an option in Auto- channel in addition to AVR mode
and it is put in action after synchronization.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
After synch,AVR keeps the gen voltage constant at the set
value. If the grid voltage is more than the gen voltage, the
pf becomes leading and lagging if the grid voltage is less
than the gen voltage.Then, in AVR mode the operator has to
reset the gen voltage so that the pf is slightly lagging.In
APF mode ,the pf always remains at the set value
irrespective of variations in grid voltage.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mohammed sajid
I can't understand your language mr.prakash,just explain
what is the function of AVR before & after synchronisation
with grid.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / balu
Once the generator connects with the grid the system voltage depends upon to the grid referrence.the active power varies depends on the load.so load varies mean time reactive power also variey.so avr will maintaine power factor after synchronization.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
It is possible to have the changeover from AVR to APF mode
automatically on synchronization / closing unit CB and the
vice versa, using auxiliary switch of the breaker.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
It keeps the gen voltage the same at the set value
irrespective of variation in speed , load and grid voltage
after synchronization. It is useful whenever there is grid
failure as the gen speed suddenly increases to an extent
depending on the load interrupted.Then AVR does not allow
for rise in voltage.It is also very helpful while
synchronizing as you do not have to vary the excitation
every now and then ,once you have matched the voltages.If
you desire to keep the pf constant after synch and loading
,you have to switch over to APF mode from AVR ,both being
available with Auto channel.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / it might be for easy calculati
It might be for
easy
calculation:-)
Is This Answer Correct ? | 2 Yes | 3 No |
Why the suply frequency in INDIA is 50HZ
What are thermo couple cables and where they are used.
Is there any Institution for giving M-tech in Electrical engineering for those who r in service? Give the details please.
What are the probable causes for failure of heating elements
WHAT IS THE SIGNIFICANCE OF VECTOR GROUPS IN TRANSFORMER? WHAT WILL BE EFFECT WHEN PHASE DISPLACEMENT CHANGES IN TRANSFORMER?
5 Answers ABB, Nissi Engineering Solution, NSL Sugars,
what are the causes for strip heater failure ?
if a damaged 500kva transformer with %impedance 2.6 is replaced by two transformers of 250Kva with different % impedance will they be able to catter the load. what will be the ratio of load on the two transformers if the % impedance is in the ratio 1:2
PLZ SEND ME SOME UNIQUE PROJECT OF ELECTRICAL ENG (B.TECH)
why number of stator and rotor slots are not equal in IM?
string efficient is 100% what is the voltage across the each disk?
How to determine the breaking capacity such as break down current and break down voltage for VCB and CT's.
What is Bolted fault?