Answer / arun 9865576777
Transformer Commissioning Work
Preliminary Test
1. HT Switchgear End
 HT BKR IR Value
Open Condition Closed
Condition
R-RI= R-Y=
R-E=
Y-YI= Y-B=
Y-E=
B-BI= B-R=
B-E=
2. Transformer end
 TRF IR Value
Note: - Neutral earth should be open
LV line PT fuse& earth link open
15sec 60sec 600sec PI
HV-E
LV-E
HV-LV
After the above tests put back neutral earth line pt fuse&
earth link Connection properly.
3. LV Panel End
 LT BKR IR Value
Open Condition
Closed Condition
R-RI= R-Y=
R-E=
Y-YI= Y-B=
Y-E=
B-BI= B-R=
B-E=
Preliminary Checks
1. HT Switchgear End
 Check Relay Setting
 Check Tightness Of CT TB
 HT Cable Connection
 Interlock Trial
 Stability Check
 BKR Trial In Test Mode
 Check Fuse
 Check MTR Operation
 Reset The All Relay
 Check Control Supply
 Reset Max Value On Relay
2. Transformer End
 TRF Body Earth
 TRF Neutral Earth
 HT Cable Connection
 Check Tightness Of CT TB
 Check WTI,OTI (or) Door Inter Lock Trial
 Check OTI,WTI Setting
 LV Side Flexible Tightness
 Check Marshalling Box Control Supply
3. LV Panel End
 Check Relay Setting
 Check Tightness Of CT TB
 LV Side Flexible Tightness
 Check Line PT Fuse
 BKR Trial In Test Mode
 Check Control Fuse
 Check MTR Operation
 Check U/V Trip Throw Line PT
 Reset The All Relay
 Check Control Supply
Before Charging
 Line PT should be in service
 LV BKR should be open condition
After TRF Charging
 Note Down Electrical Parameter In HT Side & LT Side
 Phase Sequence In LT Side
Is This Answer Correct ? | 1 Yes | 1 No |
how to calculate full load current of transformer & induction moter ?
How many size of cable required for a 300m long and 30kw inductive lode
What do you mean by S.F.U. unit? application of it.
In 3phase supply Voltage will come around 370v then what will happen?(mean what will effect on electrical equipment like AC,UPS,Motors.)
dear sir/madam i want to get some knowledge about RRB EXAMINATION(section engineer) 1- what is minimum cut off 2- wht portion is major portion . 3- can any body provide Sample paper. thanks & regards ashish
what is relation between HP & BHP
what is the diffrent between ups and inverter
What is George phenomena to start the synchronus machine?
How to check AC & DC Choke
why voltage rating of transformers are in multiples of 1.1?
What is the meaning of floating point earthing in battery backed systems ?
how to control dc motor?