what are check points to be checked while charging
switchyard?(CT,PT,BREAKER,POWER TRANSFORMER)
Answer / arun 9865576777
Transformer Commissioning Work
Preliminary Test
1. HT Switchgear End
 HT BKR IR Value
Open Condition Closed
Condition
R-RI= R-Y=
R-E=
Y-YI= Y-B=
Y-E=
B-BI= B-R=
B-E=
2. Transformer end
 TRF IR Value
Note: - Neutral earth should be open
LV line PT fuse& earth link open
15sec 60sec 600sec PI
HV-E
LV-E
HV-LV
After the above tests put back neutral earth line pt fuse&
earth link Connection properly.
3. LV Panel End
 LT BKR IR Value
Open Condition
Closed Condition
R-RI= R-Y=
R-E=
Y-YI= Y-B=
Y-E=
B-BI= B-R=
B-E=
Preliminary Checks
1. HT Switchgear End
 Check Relay Setting
 Check Tightness Of CT TB
 HT Cable Connection
 Interlock Trial
 Stability Check
 BKR Trial In Test Mode
 Check Fuse
 Check MTR Operation
 Reset The All Relay
 Check Control Supply
 Reset Max Value On Relay
2. Transformer End
 TRF Body Earth
 TRF Neutral Earth
 HT Cable Connection
 Check Tightness Of CT TB
 Check WTI,OTI (or) Door Inter Lock Trial
 Check OTI,WTI Setting
 LV Side Flexible Tightness
 Check Marshalling Box Control Supply
3. LV Panel End
 Check Relay Setting
 Check Tightness Of CT TB
 LV Side Flexible Tightness
 Check Line PT Fuse
 BKR Trial In Test Mode
 Check Control Fuse
 Check MTR Operation
 Check U/V Trip Throw Line PT
 Reset The All Relay
 Check Control Supply
Before Charging
 Line PT should be in service
 LV BKR should be open condition
After TRF Charging
 Note Down Electrical Parameter In HT Side & LT Side
 Phase Sequence In LT Side
| Is This Answer Correct ? | 1 Yes | 1 No |
Neutral CT for 45MVA 132/11 KV YNd11 Transformer. NCT REF CLASS-PS or 5P20 with 20VA burden which is suitable.
why we use end termination kit for ht xlpe cables
What Should I Know about Metering, Switchgear and Panels?
why ohms law does not obey semi-conducters?
If we need4× 50mm sq cable but it's not available so we can pull 4×25mm sq 2cables
what is pressure relief valve?where it is used????
If single phase supply is 220v. then why three phase supply is 660?
what is the full form of MEMO? name of memo train.
what is the effect of power factor to (a) voltage (b) transformers (c) generators (d)transmission lines
can indirect loading be called as phantom loading?
deisel generators all elcetical calculation formule's
What are the effects of adding a zero to a system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)