In transformer which temp should be less oil temp are
winding temp?
Answer Posted / vishal ingle
in normal condition, oil temperature should be less
compared to winding temperature because transformer oil is
used for cooling the winding. oil takes away the heat from
winding resulting in reduction of temperature. Also for
natural heat flow the oil temperature should be less than
winding temperature.
Is This Answer Correct ? | 10 Yes | 3 No |
Post New Answer View All Answers
how electrical earthing maintenance done in industry?
when it is possible kvrah lead & fundamental kwh be equal in electonic trivector meters (3 ph)
What is resistance of 50meters, 16sq.mm, single core copper cable?
What is Instantaneous Earth fault relay,how will work
Why derivative controller is not used in control systems?
63MVA,220KV/6.9KV Transformer LV side neutral is connected to Earth pit through NGR. Whether this earth pit required to connect with near by below grouding earth mat or it is to be kept separate?
What effect does a very low impedance have on the Voltage regulation? On the short-circuit current?
For electrical designers what are the standard should know? i want learn about this standards. how to get information/reference. anybody help in this regards please.
how to calculate units consumption for a 12 hp motor /hr.
Briefly describe your ideal job?
What is difference between Harmonic and Non harmonic Capacitor Bank?
Why should we hire you over the others waiting to be interview?
what is a speed of rotor when we give supply to stator of 50hz and as well as rotor of 60hz of an induction motor?????
what is the pulse and audio frequency transformer? what is different between induction regulators and tap changing transformer?
If mutual flux is 1.2wb & power factor is 0.8 lag , then what is the Useful flux of a transformer?