what is procedure of calibration of remote seal
transmiter, botom to top flanch 850mm, fluid liquid
density .73, transmiter fixed on a fractionation colum,
under vaccume 10mbar
Answers were Sorted based on User's Feedback
Answer / yomama
Your question suggest you are using a "Differential Pressure
Transmitter" in which case since the -10 Bar vacuum is
applied to both the Hi and Low legs the -10 Bar vacuum is
neutral the Transmitter
In that case we merely multiply the distance (850 mm) x (.73
SG) = 620.5
Is This Answer Correct ? | 1 Yes | 0 No |
If you installed the remote seal transmitter at flanges,
then in case empty tank /vessel, the transmitter will
showing -mA. so do the followings:
1. Make transmitter 4 mA in this case(without any pressure,
only lower low leg remote seal pressure acting)
2. Apply 850 x 0.73 =620.5 mm of water to high side of
transmitter flange and set transmitter out put 20 mA.
aftabmazari@yahoo.com
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / yomama
Your question suggest you are using a "Differential Pressure
Transmitter" in which case since the -10 Bar vacuum is
applied to both the Hi and Low legs the -10 Bar vacuum is
neutral the Transmitter
In that case we merely multiply the distance (850 mm) x (.73
SG) = 620.5
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ys
close the both hp and lp iso valve(so that any pressure
should not act on tx diaphragm). now measure the input
pressure in mm by connecting hand communicator to tx.. this
is the LRV.now measure span(ie here it is 850mm).multiply
span with liquid density(ie 850*0.73).we will get 620.5.
this is your URV
Is This Answer Correct ? | 0 Yes | 0 No |
What is Trim?
plz exlain the dcs system of ABB sympony hamnony
what sud u do if u dont get feedback from control valve?
Why the industry's standard current standards are from 4mA to 20mA,not from 0mA or any other range?
Explain the functions of the CPU of a PLC.
what are the diff. in servo and regulatory control?
Why we are using 4-20 mA as Analog signal transmission other than 3 to 19 or 2 to 18 or 6 to 22 like wise ? What is the reason behind using 4 & 20 mA? Can anyone give proper technical reply ?
HOW MANY METHODS OF TEMPERATURE MEASUREMENT ? HOW MANY MEASURING DEVICES / TRANSDUCERS ?
6 Answers Aramco, IOCL, JP Group, NFCL,
why pressure 3-15psi is used as industrial standard and what is the reason
2 Answers JAL International, UltraTech,
how to adjust relay in smart positioner ?
how the transmitter send MA?
How to calibrate electronic type level switch low?