How much Resistance Show by RTD(PT100) when it is installed in process(Consider Process Fluid temp 29 Deg C)?
Answers were Sorted based on User's Feedback
Answer / ashwin patel
111 ohm as,
Rt=R0(1+αt), where α=0. 00385, R0=at 0°=100ohm resistance for PT100,
Rt=100(1+(0.00385*29))
Rt=100(1+0.11)
Rt=100*1.11
Rt=111ohm
Is This Answer Correct ? | 3 Yes | 0 No |
what is plc? Basic function of plc? application of plc in industry? What is lader diagram ? What is the main advantage to use plc in industry?
canu tell me why 4-20 ma and why not this 3-25ma?please give reason of this value.
what is difference between E/P positioner and I/P positioner. Why E/P fixed in below actuator and why I/P fixed in other place
how to calculate MMWC values in to Tonns(MMWC values showing in DP transmitter and Tonns value showing in Totalizer). please tell me details?
I work on a electronic positioner transmitter 4211 at the field.I connect my multimeter in series to get the current output then I calibrate it to 4ma in 0% of position of the valve and 20ma in 100% position of the valve.My problem is in the field I get the correct output current based on my multimeter but in the dcs they only receive 40% in a output 20ma of this positioner.Then I try to simulate in this analog card and they receive the equivalent percent on the value that I simulated.Is ther any possibility to reset the zero and span of this positioner 4211 fisher.And what other possibility I can do to fixed this.This is my email add ( landicho_randy@yahoo.com )
What is difference between converter & transducers?
IF I WANT TO BUY A THERMOCOUPLE THEN WITCH PARAMETER I LOOK
why we are using orfice plate? then difference between orfice 7 nozzle plate?
1 Answers Flour Tech Engineers (P) Ltd,
What is the procedure of changing a Faulty Module of Allen Bradley PlC without stopping the Process
Describe a time when you anticipated potential problems and developed preventive measures.
control valve in manual/auto mode huntting checked spring tention also it is ok.positioner also good condition & incoming inst air line also constant pr.kindly give us correct answer?
How can we calibrate the level interface for Fisher® FIELDVUE® DLC3000?if use water to calibrate and our liquid SG are 0.75 and 1 ,Displacer height=14" and How much should be set SG in trasmitter during calibrate,for URV and LRV how shold be set