Answer / kiran shelar

around 110 to 112 ohm as room temp

Is This Answer Correct ?    3 Yes 0 No

How much Resistance Show by RTD(PT100) when it is installed in process(Consider Process Fluid temp 2..

Answer / ashwin patel

111 ohm as,
Rt=R0(1+αt), where α=0. 00385, R0=at 0°=100ohm resistance for PT100,
Rt=100(1+(0.00385*29))
Rt=100(1+0.11)
Rt=100*1.11
Rt=111ohm

Is This Answer Correct ?    3 Yes 0 No

How much Resistance Show by RTD(PT100) when it is installed in process(Consider Process Fluid temp 2..

Answer / dspmuthu

111.165 ohms,

Is This Answer Correct ?    2 Yes 0 No

How much Resistance Show by RTD(PT100) when it is installed in process(Consider Process Fluid temp 2..

Answer / sunny sharma

110

Is This Answer Correct ?    0 Yes 1 No

How much Resistance Show by RTD(PT100) when it is installed in process(Consider Process Fluid temp 2..

Answer / sunny sharma

100.74

Is This Answer Correct ?    0 Yes 4 No

Post New Answer

More Instrumentation Interview Questions

what is plc? Basic function of plc? application of plc in industry? What is lader diagram ? What is the main advantage to use plc in industry?

15 Answers   Schlumberger,


canu tell me why 4-20 ma and why not this 3-25ma?please give reason of this value.

6 Answers  


what is difference between E/P positioner and I/P positioner. Why E/P fixed in below actuator and why I/P fixed in other place

1 Answers  


how to calculate MMWC values in to Tonns(MMWC values showing in DP transmitter and Tonns value showing in Totalizer). please tell me details?

2 Answers   Chemin C I, MSP,


I work on a electronic positioner transmitter 4211 at the field.I connect my multimeter in series to get the current output then I calibrate it to 4ma in 0% of position of the valve and 20ma in 100% position of the valve.My problem is in the field I get the correct output current based on my multimeter but in the dcs they only receive 40% in a output 20ma of this positioner.Then I try to simulate in this analog card and they receive the equivalent percent on the value that I simulated.Is ther any possibility to reset the zero and span of this positioner 4211 fisher.And what other possibility I can do to fixed this.This is my email add ( landicho_randy@yahoo.com )

4 Answers  






What is difference between converter & transducers?

4 Answers  


IF I WANT TO BUY A THERMOCOUPLE THEN WITCH PARAMETER I LOOK

1 Answers  


why we are using orfice plate? then difference between orfice 7 nozzle plate?

1 Answers   Flour Tech Engineers (P) Ltd,


What is the procedure of changing a Faulty Module of Allen Bradley PlC without stopping the Process

1 Answers   Siemens,


Describe a time when you anticipated potential problems and developed preventive measures.

0 Answers   Hotel Management,


control valve in manual/auto mode huntting checked spring tention also it is ok.positioner also good condition & incoming inst air line also constant pr.kindly give us correct answer?

5 Answers   Madhu Power,


How can we calibrate the level interface for Fisher® FIELDVUE® DLC3000?if use water to calibrate and our liquid SG are 0.75 and 1 ,Displacer height=14" and How much should be set SG in trasmitter during calibrate,for URV and LRV how shold be set

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)