Furnace draft transmitter range is -50 to +50 mmwc. why the
impulse line connected in hp side?
Answers were Sorted based on User's Feedback
Answer / carl_ellis
A draft range measurement is typically a gauge pressure
measurement, referenced to atmosphere.
Draft range is very, very low pressure, so DP transmitters
are typically used because they're readily available in
a 'draft' range with the large diaphragms necessary for low
pressure measurements.
The high side is connected to the process with an impulse
tube. The low side is exposed to atmospheric pressure.
Good practice puts a filter, like a scintered pneumatics
filter on the low side, so that dirt doesn't fill the low
side cavity and air movement (wind, passing vehicles) is
buffered and damped to prevent the forces of air movement
on the low side from affecting the draft measurement.
If the impulse line were connected to the low side, the DP
would be negative, a DP subtracts the low side pressure
from the high side pressure (atmosphere minus some positive
pressure = negative pressure). Convention says that draft
range is positive so the impulse connection is to the high
side, to get a positive value.
Tell 'em Carl sent you.
Is This Answer Correct ? | 12 Yes | 1 No |
Answer / deepak
Dear Carl,
Cant we use an Absolute pressure transmitter ?
Is This Answer Correct ? | 1 Yes | 0 No |
Describe a time when you anticipated potential problems and developed preventive measures.
In control valve there are two type of valve seat we can use metal to metal seat & soft seat.On this valve seat i have following doubt. 1)I have never seen practically the internal assembly of valve so my doubt is that basically weather the seat is soft seat or metal its basic MOC is same as valve body(SS or CS) only in soft seat we are using PTFE ring & place on valve seat & in metal this PTFE ring is not threr am i correct??????? 2)what are the common general rule for using metal to metal seat & soft seat,means its depend on process parameter like liquid,gas, steam & on valve leakage class.
how to measure temperature from resistance of rtd?and how to measure temp from voltage of thermocouple?is there any formulas?
how to calibrate load cell
what is the function of a zener diode ?
If we increase only P what will be controller action ?
3element
We have a Yokogawa Micro-XL DCS, which is having around 300 I/O, but whenever there is any wire gets grounded in field, the 24v supply to all loops gets dipped & all the indications at DCS goes to IOP(shows input open), at present we have fixed 500mA fuses in all the lines but which does not working. Does it required to replace with lower amps fuse, then how much or is there any other solution for this.
what is compensation? temprature & pressure
What is the electronic transmitter frequency.
WHAT IS THE MASS FLOW FLOW METER
what are the inputs (drawings) we need to prepare loop schematics??