after syncnhronistion how generator speed controlled by grid
Answers were Sorted based on User's Feedback
Answer / arjunyadav
the generator speed cannot varied ofter synchronisation
because if the speed varies then the frequency varies if we
change the speed then the over or under frequency relay
will operate and trips the circuite.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
The grid is more powerful than the generator or the
station.The speed of any generator is decided by the grid
while synchronizing or running.3 % variation in frequency is
allowed as per IE rules.
| Is This Answer Correct ? | 2 Yes | 1 No |
The generator is magnetically coupled to the grid
frequency. If the fuel to the generator is increased the
generator will try to increase speed but as it is
magnetically locked to the frequency it will take more load
instead. The reverse will happen if the fuel is decreased.
Under some circumstances the magnetic coupling can be
broken. If this happens the energy from the grid will try
to drive the generator back into synch. This can cause
extensive damage to the generator and/or switchgear.
Therefore protection should be used to stop this from
happening.
| Is This Answer Correct ? | 0 Yes | 0 No |
what's the different between ELCB, ELR and ELS?
SUTIABLE FOR ohm's law super conductor
What is the need of motor starter?
What will be the capcity of 3 phase DG set require for 25 KVA single phase lighting load?
Hi, This is Laila. I am selected for syndicate bank interview. Could you please share your views and the questions asked if you have faced the interview My email id is laila_honey09@yahoo.com Please send as fast as u can.Thank You Thanks... Laila.
why ground cannot be used as neutral as ground also provides close path for current flowing ?
What is the basic principle of operation of alternators/dc generators?
A generating system will have a total capacity of 300 MW. Find the probable forced outage when the capacity is supplied by two 150 MW units. The operating probability of all units is P=0.98 and forced outage probability rate Q =0.02 .
What is the difference between rated and per unit in transformer?
how many minutes or seconds taken by the transmission of electrical power from generating end to distributing end?
A 3PH MOTOR RUNNING IN NORMAL CONDITION AND ITS AMPERE ALSO UNDER ITS FULL LOAD CURRENT,ITS CABLE RATINGS ALSO HIGER THN ITS CAPACITY,BUT ITS CABLE GETTING ABNORMAL HEAT(NOT TOO HOT)WHY ITS GETTING HOT LIK THIS?
Can the same motor be operated in both direction ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)