why is the vector group analysis done in transformer tests
Answers were Sorted based on User's Feedback
Answer / ganeswar sahu
To check the phase angle displacement between two
windings of a manufactured traformer and to check whether
internal winding connection is matching to the vector group
as mentioned in the name plate .
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / raju.t
1. To check the phase angle displacement between two
windings of a manufactured trafo.
2. To check the correctness of vector group mentioned in
the name plate of trafo and actual connection.
Is This Answer Correct ? | 12 Yes | 1 No |
Answer / jagdish krushnarao zeliye
vector group of transformer is used to know the phase angle
for parallelling operation
Is This Answer Correct ? | 13 Yes | 5 No |
Answer / saba anjum
vector group are made to know at what position the secondary
winding of transformer we get star and delta voltages . and
it indicates the type of winding in primary and secondary
which helps in parallel operation of transformer with
different ratings having same vector group .
Is This Answer Correct ? | 13 Yes | 7 No |
Answer / purav solanki.
for the parallel operation of two transformer.
Is This Answer Correct ? | 13 Yes | 8 No |
Answer / usama badran ali
vector group analysis used for two important things?
1-it describes the charcteristic of transformers...how?
1-primary and secondary connections.
2-low and high voltage sides.
3-leading angle between high and low voltages.
2-to connect two parallel transformer, you should know the
line to line voltages of two transformer (i mean each
similar line voltages of the parallel transformers ).
3-in the modern technolgy of power electronics in three
phase inverters i can eleminate fixed order of harmonics by
changing the transformer connection .
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / saksh
to check the phase angle displadement so as to know the
power factor itis lag or lead
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / kulu
TO Check the phase displacement between HV winding and Lv
winding
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / ramama
for parallel operation of two different rating transformers
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / ganesh nayak
Vector anlysis is done to check whether the transformer
under test is suitable for parallel operation with another
transfomer having same vector group and voltage ratio but
difference in KVA rating.And to know the phase displacment
and polarity of the transformer.
Is This Answer Correct ? | 2 Yes | 1 No |
give information about REM5453 & SPAJ Relays
what is deffrence between squirral cage and wound rotor in IM?
could any one explain me what power factor and where it is use ful
Formula to calculate fault current flowing in the neutral line?
i have one transformer 1000kva, 11/.433kv. we are using 200/5 amp. ct unit for measuring purpose, & one 800 amp. V.C.B Unit for the same t/f operate, i wants to known the primary current of T/F is only 53 amp. why we used 800 amp. V.C.B ? & 200/5 amp. CT Unit.
What facility we get after CT secondary earthing and how?
how to select short circuit current while selecting a MCCB? how to calculate current for a given KVA and KW load?
2 Answers GE, PnU Engineering,
What is Earth Fault and Over current Fault.
In LT Line What is the minimum clearance required between phase to phase busbar & between Phase to body of the panel? Also between Neutral &phase, & Neutral & body of panel. as per standards.
Why we use a shunt capacitor or synchronizing Motor To Improve a Power factor pls reply me in this mail dinesh_elect_eng@yahoo.com
how works inductive &capacitive sensors?
2 hp motar how many amps taken please show me the formula