if i change range of flow transmitter in th field then does
it need to change range in dcs?
Answers were Sorted based on User's Feedback
Answer / murali -inst.technologist
if range of transmitter changes in field you have to change
the span of the AI in dcs
other wise
transmitter shows correct reading in field side
but dcs get signal in form of 4-20 ma, then flow reading
shows in DCS is as per old DCS span.
Is This Answer Correct ? | 12 Yes | 1 No |
Answer / www.islamqa.com
we have to configure the range in dcs with the new values.
example:
old range:
o - 625 "wc means 4ma at 0, 20 ma at 625
new range:
0 - 2500 "wc means 4 ma at 0, 20 ma at 2500
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
ahmedsabry.online@gmail.com
CELL.: 00 2 0121367310
Is This Answer Correct ? | 8 Yes | 0 No |
can any one pl explain me in brief that how we select the leakage classification in valve,means for liquid or gas there is any standard for selecting leakage classification or its depend upon valve size or any any other parameter.
How to do gas analysers calibration in AUTO and Manually by using zero and span gas?
how to convert MA in to measuring values..and how mwasuring values into MA ?..plz ansr.i have intervw
How will you calibrate an interface level trol/normal level trol in line and in w/s?
Why we use the remote seal transmitters
what is temperature compensation?
Why using negative voltage in vibration measurement?
What is the difference between floating and fixed voltage?
radial & axial vibration sensor output voltage is ac or dc volt?
PLZ explain to me massflow
What is shielding effect?
0 Answers Process Control Technologies,
What properties or parameters to be taken into consideration for protection while selection of Dcs controller.