Answer / mathan
loop checking means ,after installation of instruments we
must check full loop(instrument-junction box-control room)
to ensure that whether the instruments are working properly
or not, and whether is it passing the signal or not,whether
is it receiving the signal or not. before we start the
plant we need to check loop..
during the loop check we give some known input
and check the corresponding output at other side(control
room)..if the output is corresponding to input, the loop is
ok..if not means, something fault inbetween the loop.
for example.if you want to check ON/OFF control
valve,during the loop check,when you give 24v dc from
control room ,the valve must open fully, and when you give
0v dc the valve must close.
Is This Answer Correct ? | 274 Yes | 10 No |
Loop Checking means, First we want to check the continuity
of cable. Then whether 24 V DC or 4 - 20 mA DC is coming
from DCS or JB want to check. That is called loop Checking.
Is This Answer Correct ? | 132 Yes | 18 No |
Answer / rovel delalamon
loopcheking, field to the control room.from instruments to ijb.formijb to mrashalling cabiet.,,check polarities,check the voltage suplly w/24v dc. chech also the possible leaks of the tube.and warm-up 5mins.prior to calibration.use HART COMMUNICATOR.highway addressable remote transducer.the one who configuer the input and output of the trnsmitter
Is This Answer Correct ? | 42 Yes | 17 No |
Answer / shreeyash nandurkar
Loop Checking
Some think of loop checking as
a process to confirm that the
components of the loop are wired correctly and is typically
something
done prior to start-up. However,
due to factors described in the
introduction above, the loop check’s
scope has expanded to also include
tests to confirm that it is “operating as designed” and then
to ongoing
programs for benchmarking and monitoring performance. The block
diagram in Figure 1-5 illustrates the
components of this expanded loop
checking process.
This process starts when the instruments are received at the
plant site.
It continues through installation and
start-up and into the ongoing plant
operation. In addition, the control system should perform
the intended
function properly. This includes
verifying the transmitter’s process
variable (PV) for display to the operator, for use in the
control strategy,
and for historical trending. This verification testing prior
to start-up is
known as the factory acceptance test
(FAT) which, as an option, can be
duplicated at site with the actual hardware and software
installed, termed
site acceptance test (SAT). Further discussed in Chapter 2,
the FAT can be
performed prior to shipment of the
hardware or in parallel with the
hardware installation
at site if the overall start-up schedule is compressed.
Once the technician checks the control strategy to verify
that the
expected output to the final control element is produced,
the loop can then
be commissioned and start-up can proceed.
Finally, the loop check can include defining the loop
performance
benchmark and providing a method for monitoring the
performance over
time.
Is This Answer Correct ? | 11 Yes | 3 No |
Answer / md mahtab khan
loop checking as a process to confirm that the
components of the loop are wired correctly and is typically something done prior to start-up.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / rodel baluyot
LOOP CHECKING IS CHECKING 4 TO 20 MA OUTPUT FIELD AND CONTROL ROOOM
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / azarudeen
Loop checking is nothing but Checking continuity.
Is This Answer Correct ? | 20 Yes | 72 No |
Answer / surya
I think loop checking is another way of calling "feedback"
...
m not sure abt it..
Is This Answer Correct ? | 19 Yes | 81 No |
Why we are using PLC instand of DCS in ESD System? can u explain any one?
While preparing the graphic diagrams trend display, 3 types of trends are prepared by Yokogawa system vender. These are for process variable, manipulated variable & set point variable. Why these 3 trends are required? Explain the purpose of these 3 trends.
what is consistency transmitter and describe its working?
What is minimum distance between three thermocouples (2oo3) mounted on same pipe line (20")? Technically accepted by stright line mounted or circler mounted?
Is there a particular problem if two proposals from the same observatory (originating with different partners) are submitted?
Why in turbine used two critical speed band ?
Pressure transmitter working Principles?
Why do we have earthing cable in branch cable and shield in the same cable?
0 Answers Process Control Technologies,
I want to install analog type, flange mounted gas flow meter (line size - 2"), for CNG flow measurement.Kindly give some details of flowmeter or suppler name, available in India.
is any standard angle for thermowell mounting for horizontal and vertical pipe lines?
how to install the Ph and Conductivity analyser? is there are any procedures which has to be maintained.
why we are not using the turbine flow meter in the steam service?