How to isolate a DPT from line in the condition that process
must not be disturbed,and process is also critical and no
bypass is available.?
Answers were Sorted based on User's Feedback
Answer / lal
we can set the actual value & activate a Timer from the DCS , within in the time which set on the DCS we can isolate the transmitter from the line , and it will not affect the process , the timer is used for safety purpose , we cannot activate it more than a limited time.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / muhammad arsalan afzal
isolate the transmitter from the main isolation valve and
follow this procedure.
First of all
1= Close high pressure manifold valve
2= open the equilizing valve
3= than close the low pressure manifold valve.
Mostly we we open equilizer valve when we are isolating
the tx. but what will happen if we close high side pressure
valve before equilizing valve? applied process Pressure is
already there on both sides of the transmitters no extra
pressure will be exerted on the tx because we are only
closing the valve. DP cell demage only in that case if we
purge high or low side before closing the manifold
isolation valves and we start closing the valve without
opening the equilizer.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinu joseph
first close the process isolation valve.then slowly equlise the pressure using equalising valve in the manifold.thendrain the transmitter and we can remove it from service
Is This Answer Correct ? | 4 Yes | 5 No |
Answer / m.abouraya
1-open the equalizer and then open the isolation valves
(high wth low) and then make the drain
Is This Answer Correct ? | 1 Yes | 5 No |
How to adjust the zero & span of a control valve from the posiitioner(MIL)?
what is difference between two wire &three wire pt 100 ?
What is safety barrier and how it is work
I am pujita completed Electronics and Instrumentation Engineering.As a fresher i am going to attend the interviews.Could anybody guide the topics/questions covered mostly in interviews.
how many mmwc are eual to 1kg/sq.cm & can we calculate mmwc into tph?
how to connect transmitter measuring sulfur process? 1-by using long impulse line or 2- by using coated short impulse line
ABB DCS (AC 800 M)redundency take howmany milliseconds to switch from master controller to slave?should be less than DCS scanning time?
Steve said that "An eddy-current probe works by passing an alternating current through a coil of wire and measuring the coil’s impedance" while we are using -24 Volt DC , So I am confused about DC and AC. Plz .
2 Answers Jindal, Sadara Chemicals,
Can i convert 230v ac to 24v dc by using a relay?Instead of Smps is it possible? What is relay logic in plc ?? How it works?
what is hall effect?where it is use in power plant?
If I installed wrong directions orifice plate then what showing value d.p transmitter?
IF I WANT TO BUY A THERMOCOUPLE THEN WITCH PARAMETER I LOOK