1 ton AC takes how much current( starting & stable)
Answers were Sorted based on User's Feedback
Answer / ahmed alyassi
My friend if we assume the normal.current is 7 amps
Then due to that split ac is considered it is inductive load
The starting current would be x5 or x4 more
So . 7 times 4 =28 amps
But even if your breaker is 25 lets assume
It might not trip. Immediatly cause the delay and the amps didnt increase alot
I would recommend 32 A for 1ton or 1.5ton
| Is This Answer Correct ? | 20 Yes | 23 No |
Answer / lalitha
1ton=3.5168kW,
I=p/vcos(theta)
I=3.5168/230*.95
=16.09
For power factor of 0.85 current is 17.98
So to even consider initial rush of current 20A breaker is used
| Is This Answer Correct ? | 16 Yes | 19 No |
Answer / pawan
dear friend 1TR - 1200WAT= 1.2 KILOWATT
AND watt=v*i
I= W/V =1200/240=5 AMP
YOUR ANS IS 5 AMP DEAR
| Is This Answer Correct ? | 13 Yes | 19 No |
Answer / raghavendran
A 1 ton AC consumes 3.5KW of power.so under running
condition we can estimate the current consumed as
3500/(230*.8 say)
| Is This Answer Correct ? | 26 Yes | 35 No |
Answer / nikunj
1 TR = 3.51 kw
Now as per formula, P = V x I x COSphi,
I = P / (V x COSphi) for single phase,
I= P / (1.73 x V x COSphi) for three phase, so you can
easily calculate the current rating required.
| Is This Answer Correct ? | 17 Yes | 26 No |
What are the advantages of instrument transformer?
Can we calculate the P.F if we know the only load on alternator .
why T/F winding temp measurement cts are odd secondary current ie,109A/1.2A/1.4A?
0 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
Why 1/3 is used in symmetrical components?
What will be the capacity of the generator set which can be used for my 2 ton window air conditioner ?
What is an ideal transformer?
Ohm's law applicable for semi-conductors?
why DG,Transformer,UPS capacity will be tell in KVA but not in KW?
what is V.L.F. testing of power cable? do you know the voltage ratings, like for what rating and size of cable what rating of V.L.F. testing is used?
What will happen if the generator turns in a wrong direction?
In Slip ring Induction Motor we use Liquid Rotor Starter for Starter Every Time Liquid Filling we need add Soda Sodium Carbonate or only Distilled water is Enough.
please explain me about traction application?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)